Firmware Update on ISX PDU (PDRPPNX14-M1)

Solved
SD_James_apc
Crewman
Crewman
0 Likes
9
249

Firmware Update on ISX PDU (PDRPPNX14-M1)

This was originally posted on APC forums on 5/8/2007


I can get to the PDU on the network.
Current firmware is xpdu-2.0.1, aos-2.6.4

It isn't recognized by ISX Mgr as a valid APC device. I figure the firmware needs to be upgraded, but can't find any information on where to get the firmware to do the upgrade.

Where do I get the upgrade, if there is one? Or should I post in the ISX Mgr forum?


Accepted Solutions
Sgt._Slaughter_apc
Lt. Commander
Lt. Commander
0 Likes
0
249

Re: Firmware Update on ISX PDU (PDRPPNX14-M1)

This was originally posted on APC forums on 5/8/2007


Your Firmware is the newest available for the ISX PDU. Try resetting the boot mode as suggested above.

Thanks.

See Answer In Context

9 Replies 9
SD_James_apc
Crewman
Crewman
0 Likes
0
249

Re: Firmware Update on ISX PDU (PDRPPNX14-M1)

This was originally posted on APC forums on 5/8/2007


Actually, this is the full rack PDU for InfraStruXure, not the PDU power strips. Search the site for PDRPPNX14-M1.

dirtfoot_apc
Lt. Commander
Lt. Commander
0 Likes
0
249

Re: Firmware Update on ISX PDU (PDRPPNX14-M1)

This was originally posted on APC forums on 5/15/2007


I believe the PDU needs to be on the private side LAN of the ISX Manager. Then, the ISX Manager should provide it with an IP, and recognize it as a valid device. I do not beleive this PDU will be recognized properly if it is connected to your public LAN.

SD_James_apc
Crewman
Crewman
0 Likes
0
249

Firmware Update on ISX PDU (PDRPPNX14-M1)

This was originally posted on APC forums on 5/8/2007


I can get to the PDU on the network.
Current firmware is xpdu-2.0.1, aos-2.6.4

It isn't recognized by ISX Mgr as a valid APC device. I figure the firmware needs to be upgraded, but can't find any information on where to get the firmware to do the upgrade.

Where do I get the upgrade, if there is one? Or should I post in the ISX Mgr forum?

BillP
Administrator Administrator
Administrator
0 Likes
0
249

Re: Firmware Update on ISX PDU (PDRPPNX14-M1)

This reply was originally posted by Deric on APC forums on 9/25/2007


We have the same problem at our Data Centers. There are three 80's now in the plant with none of the ISX PDU's have the ability to work with APC Manager in the regular coporate network. If they are placed in the private networking area, they are fine. It would be nice to see this fixed.

Grenade_apc
Lieutenant
Lieutenant
0 Likes
0
249

Re: Firmware Update on ISX PDU (PDRPPNX14-M1)

This was originally posted on APC forums on 9/25/2007


There is a new firmware available for the xpdu, version 333. I am not sure why it's not posted on the website, but you can call into the 3 phase support line and they can e-mail it to you. This new revision does allow the devices to communicate on the public LAN

Grenade_apc
Lieutenant
Lieutenant
0 Likes
0
249

Re: Firmware Update on ISX PDU (PDRPPNX14-M1)

This was originally posted on APC forums on 9/25/2007


Another common issue I have seen with Not an APC Device is not having an IP address configured for the public port of the ISX manager, regardless of it is connected to your public network or not. You need to have an IP, subnet mask, and gateway entered.

BillP
Administrator Administrator
Administrator
0 Likes
0
247

Re: Firmware Update on ISX PDU (PDRPPNX14-M1)

This reply was originally posted by Oscar on APC forums on 9/25/2007


I've seen this before where "rebooting" the ISX MGR fixed the issue. Give it a try.

SD_James_apc
Crewman
Crewman
0 Likes
0
247

Re: Firmware Update on ISX PDU (PDRPPNX14-M1)

This was originally posted on APC forums on 5/10/2007


No luck. I changed the boot mode back and forth, tried a different IP. ISX Mgr can ping the device, but doesn't recognize it as an APC device. I'm running ISX Mgr 4.6.1 build 23

Sgt._Slaughter_apc
Lt. Commander
Lt. Commander
0 Likes
0
250

Re: Firmware Update on ISX PDU (PDRPPNX14-M1)

This was originally posted on APC forums on 5/8/2007


Your Firmware is the newest available for the ISX PDU. Try resetting the boot mode as suggested above.

Thanks.