Posted: 2021-06-28 03:28 AM . Last Modified: 2024-03-18 04:38 AM
Hi,
We have a Smart-UPS 3000 XLM and we've just added an external battery pack. I've accessed the UPS network interface and where it asks me to indicate the number of external batteries do I indicate one or two? The reason I'm not sure is because the external battery pack has two batteries in it
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:28 AM . Last Modified: 2024-03-18 04:38 AM
That's exactly right, we only have one of those. Thanks for the info!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:28 AM . Last Modified: 2024-03-18 04:38 AM
That's exactly right, we only have one of those. Thanks for the info!