Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79443members
344199posts

Event log shows incorrect time

Solved
BillP
Administrator Administrator
Administrator
0 Likes
10
654

Event log shows incorrect time

This question was originally posted by Phillip on APC forums on 4/20/2009


Hello,

My event log in the network management card shows the incorrect time. Everything I've done today is logged as 2002. How do I get the time corrected? I read something about a battery that might need replacing on the card. Does that sound correct?

I have a Smart-UPS 3000 RM

The Card model is AP9617
Hardware revision: A10

Let me know if more information is needed.

Thanks in advance.


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
654

Re: Event log shows incorrect time

This reply was originally posted by Phillip on APC forums on 4/22/2009


Here is the screenshot of the about section

See Answer In Context

Attachments
10 Replies 10
BillP
Administrator Administrator
Administrator
0 Likes
0
654

Re: Event log shows incorrect time

This reply was originally posted by Phillip on APC forums on 4/20/2009


I see the Date and Time configuration information in the help file of the web admin section, but I can't find where I can go to adjust the settings.

BillP
Administrator Administrator
Administrator
0 Likes
0
654

Re: Event log shows incorrect time

This reply was originally posted by Phillip on APC forums on 4/20/2009


I couldn't find any place in the web interface to set the time. I stepped through each setting and found nothing.

BillP
Administrator Administrator
Administrator
0 Likes
0
654

Re: Event log shows incorrect time

This reply was originally posted by Angela on APC forums on 4/20/2009


have you tried to reset the time on the data and time section of the card but it keeps resetting itself? or have you not found the section in the interface to adjust it?

BillP
Administrator Administrator
Administrator
0 Likes
0
654

Re: Event log shows incorrect time

This reply was originally posted by Angela on APC forums on 4/20/2009


i posted some screenshots. one is version 3.x firmware and one is version 2.x.

in the 3.x firmware versions, this option is under Administration->General->Date & Time->Mode->System Time Configuration (which is where you choose Manual data and time or NTP). this is seen in the attachment "3x."

in the 2.x firmware revisions (as well as 1.x if its that old), this option is under System->Date & Time->System Time Configuration. this is seen in the attachment "2x."

hope this helps! let me know if you are missing an option or it looks different.

Attachments
BillP
Administrator Administrator
Administrator
0 Likes
0
654

Re: Event log shows incorrect time

This reply was originally posted by Phillip on APC forums on 4/21/2009


Here is a screenshot of what I'm looking at. I'm thinking I am either connected to the wrong device or that I need a firmware update. Do I need to connect to any particular port? Currently I am just connecting to the IP with no port designated (so port 80 I would assume).

Attachments
BillP
Administrator Administrator
Administrator
0 Likes
0
654

Re: Event log shows incorrect time

This reply was originally posted by Angela on APC forums on 4/21/2009


hmm no you are accessing it correctly but yes, i do not see a system section on the left hand side of the screen. can you please get me a screenshot of the Help->About System screen? i know you posted part of it before but i'd like to see the entire thing.

thanks!

BillP
Administrator Administrator
Administrator
0 Likes
0
654

Re: Event log shows incorrect time

This reply was originally posted by Phillip on APC forums on 4/23/2009


Thanks IPaW! I'll give this a go and let you know the results.

BillP
Administrator Administrator
Administrator
0 Likes
0
654

Re: Event log shows incorrect time

This reply was originally posted by Angela on APC forums on 4/24/2009


awesome. no problem!

BillP
Administrator Administrator
Administrator
0 Likes
0
654

Re: Event log shows incorrect time

This reply was originally posted by Phillip on APC forums on 4/24/2009


Its all working now! Thanks again!

Attachments
BillP
Administrator Administrator
Administrator
0 Likes
0
655

Re: Event log shows incorrect time

This reply was originally posted by Phillip on APC forums on 4/22/2009


Here is the screenshot of the about section

Attachments