APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:03 AM . Last Modified: 2024-02-29 10:55 PM
Hello there , I have single APC ups with NIC , 3 Esxi host managed by vCenter appliance . I have installed the APC Virtual appliance alongside of the vCenter appliance.
After configuration host and guest Os are all shutdown gracefully but when power come back online some of the host put into maintenance mode therefore vm's are not able to power on with this mode, it happenes with only 2 host.
Can someone explain me how to stop this, APC virtual appliance also not accepting user name and password after reboot from web interface?
Thank you very much indeed in advance
Jaffa
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:03 AM . Last Modified: 2024-02-29 10:55 PM
Hi,
On 7/18/2015 3:34 PM, Jaffa said:After configuration host and guest Os are all shutdown gracefully but when power come back online some of the host put into maintenance mode therefore vm's are not able to power on with this mode, it happenes with only 2 host.
What is recorded in the PowerChute Event log? Does it record that the host are being shut down and is there any messages concerning vCenter Server? If you look in /opt/APC/PowerChute/group1 there is an error log you should review that for errors concerning the hosts. Page 107 of the PowerChute VMware Users Guide list troubleshooting steps for the hosts and Application Note 180 on page 4 lists the shut down and start up process for this configuration.
On 7/18/2015 3:34 PM, Jaffa said:Can someone explain me how to stop this, APC virtual appliance also not accepting user name and password after reboot from web interface?
The maximum number of characters for the user name is 10 and must match the NMC. The password is unique to PowerChute. The password length must be 3 to 32 characters and special characters are allowed.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:03 AM . Last Modified: 2024-02-29 10:55 PM
Hi,
On 7/18/2015 3:34 PM, Jaffa said:After configuration host and guest Os are all shutdown gracefully but when power come back online some of the host put into maintenance mode therefore vm's are not able to power on with this mode, it happenes with only 2 host.
What is recorded in the PowerChute Event log? Does it record that the host are being shut down and is there any messages concerning vCenter Server? If you look in /opt/APC/PowerChute/group1 there is an error log you should review that for errors concerning the hosts. Page 107 of the PowerChute VMware Users Guide list troubleshooting steps for the hosts and Application Note 180 on page 4 lists the shut down and start up process for this configuration.
On 7/18/2015 3:34 PM, Jaffa said:Can someone explain me how to stop this, APC virtual appliance also not accepting user name and password after reboot from web interface?
The maximum number of characters for the user name is 10 and must match the NMC. The password is unique to PowerChute. The password length must be 3 to 32 characters and special characters are allowed.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.