Hello,
I own an older UPS surt3000xl with AP9619 and a temperature probe.
From what I googled, OID .1.3.6.1.4.1.318.1.1.10.2.3.2.1.4.1 should be the one for temperature output.
Thing is, it's integer value, so no decimals are available.
On the other hand, on the webUI i'm normally seeing decimal values for the environment probe temperature output.
Is this a limitation or?
UPS FW: 450.17.W
AP9619
sumx v3.7.2
aos v3.7.3
Thanks in advance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:34 AM . Last Modified: 2 weeks ago
Hello Vladimir,
Voidstar is correct, there is no high precision OID for the temperature probe.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:34 AM . Last Modified: 2 weeks ago
SNMP only supports integers. As a workaround, some OIDs have a corresponding high precision OID that reports in tenths or hundredths. I don't see any such OIDs for the temperature probe.
To explore all the OIDs available, I recommend downloading the PowerNet MIB (from here listed as "Firmware Upgrade - MIB"). Use it with a free tool GetIF (available here) and walk the target system to see everything it supports.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:34 AM . Last Modified: 2 weeks ago
Hi,
I've expressed myself wrongly here. I am aware SNMP outputs only integers.
By integer value in output of .1.3.6.1.4.1.318.1.1.10.2.3.2.1.4.1 I meant it isn't high precision.
So far I used the high precision UPS internal battery temperature OID .1.3.6.1.4.1.318.1.1.1.2.3.2.0 but I can't seem to find the high precision version for environment probes.
I assume a high precision OID for this should be available since I see probe temperature readings in the WebUI in precision in tenths.
Can someone confirm there's no high precision OID for probe temperature values in AP9619 ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:34 AM . Last Modified: 2 weeks ago
Hello Vladimir,
Voidstar is correct, there is no high precision OID for the temperature probe.