Disable Self-Test Notifications on APC 1400

This was originally posted on APC forums on 11/12/2013


I have multiple APC 1400 RM XL UPS's that are set to self test weekly and biweekly.  I only need email notifications sent if the self-test fails, as opposed to a notification every time a self-test starts or passes.  Is there a way to disable these notifications either via web interface or telnet?  Thanks in advance.


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
494

Re: Disable Self-Test Notifications on APC 1400

This reply was originally posted by Angela on APC forums on 11/12/2013


Hello,

This knowledge base will help you -> Configuring clearing events with APC Network Management Cards | FAQs | Schneider Electric US

Just make sure to read the disclaimer in it before disabling self test passed.

See Answer In Context