I have a DLA1500i similar to SUA1500i I have been told.
I worked fine for years, apart from need battery replacing every 2/3 years it was just fine. But now it's not working as expected, aproximatly 2 out of 5 power outages it shuts itself down and drops the load. I saw it happening once, heard it beeping with the overload light on, then it turned down right after...
The load is about 20%(one light on) so I don't think it's overloaded.
Any idea about what could be causing this?
Control board defect, replaced all the eletrolytic capacitors except the big one 2700uF 40v and it's working fine now.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:28 PM . Last Modified: 2024-03-04 10:32 PM
Control board defect, replaced all the eletrolytic capacitors except the big one, 2700uF 40v, and it's working fine now.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:28 PM . Last Modified: 2024-03-04 10:32 PM
Control board defect, replaced all the eletrolytic capacitors except the big one, 2700uF 40v, and it's working fine now.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.