Critical Event in Smart-UPS SRT 8000 (SRT8KRMXLI). Distorted waveform. 0x020F

Solved
hrondon_apc
Crewman
Crewman
0 Likes
6
260

Critical Event in Smart-UPS SRT 8000 (SRT8KRMXLI). Distorted waveform. 0x020F

This was originally posted on APC forums on 2/28/2017


Dear All

I'm facing a Critical Event (distorted waveform. 0x020F)  in Smart-UPS SRT 8000 (SRT8KRMXLI). When the the Power supply is from specific MotoGenerator. The UPS is going to swich off the Outlet Group and all devices connected are facing unexpected shutdown.

Attached you can find logs and the configuration .

 

Thanks in advance

Attachments
Tags (2)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
261

Re: Critical Event in Smart-UPS SRT 8000 (SRT8KRMXLI). Distorted waveform. 0x020F

This reply was originally posted by Afzal on APC forums on 3/7/2017


dear Hector,

                 change the input settings not output settings .

thanks

See Answer In Context

6 Replies 6
BillP
Administrator Administrator
Administrator
0 Likes
0
261

Re: Critical Event in Smart-UPS SRT 8000 (SRT8KRMXLI). Distorted waveform. 0x020F

This reply was originally posted by Merick on APC forums on 3/1/2017


Hi Hector,

Sorry about the late response, but can you get me the complete logs,  you can get this from the web interface - ABOUT > SUPPORT > GENERATE LOGS, once you have the logs, I'd like to take a look at the config.ini.

Regards

BillP
Administrator Administrator
Administrator
0 Likes
0
261

Re: Critical Event in Smart-UPS SRT 8000 (SRT8KRMXLI). Distorted waveform. 0x020F

This reply was originally posted by Merick on APC forums on 3/1/2017


Checking on your configuration, your unit is setup to output 230V, and input the voltage you're getting is about 220Vs.  the load you have attached on the UPS are they set for what voltage?  The input and output voltage should be about the same so that if the UPS goes on bypass, the load attached to it won't get damage.

you can also refer to - http://www.apc.com/us/en/faqs/index?page=content&id=FA157068

Regards

hrondon_apc
Crewman
Crewman
0 Likes
0
261

Re: Critical Event in Smart-UPS SRT 8000 (SRT8KRMXLI). Distorted waveform. 0x020F

This was originally posted on APC forums on 3/2/2017


Hi Merick

 

All devices connected to both UPS can work with 220-240 V. Could you advice with your recommendation in order to solve this issue

 

 

BillP
Administrator Administrator
Administrator
0 Likes
0
261

Re: Critical Event in Smart-UPS SRT 8000 (SRT8KRMXLI). Distorted waveform. 0x020F

This reply was originally posted by Merick on APC forums on 3/2/2017


Hey Hector,

Under configuration > Power Settings > Rated Output Voltage

if you have an option for 220v, select that, now before you change the output voltage the UPS should be on stand by.

Regards

hrondon_apc
Crewman
Crewman
0 Likes
0
261

Re: Critical Event in Smart-UPS SRT 8000 (SRT8KRMXLI). Distorted waveform. 0x020F

This was originally posted on APC forums on 3/3/2017


Hi Merick

I will proceed with one UPS and we can check the performance

 

Regards

Hector

BillP
Administrator Administrator
Administrator
0 Likes
0
262

Re: Critical Event in Smart-UPS SRT 8000 (SRT8KRMXLI). Distorted waveform. 0x020F

This reply was originally posted by Afzal on APC forums on 3/7/2017


dear Hector,

                 change the input settings not output settings .

thanks