We have fairly regular power issues, and the constant beeps of our Symmetra 8000 are becoming annoying.
I only found 3 settings relating to alarms (all in one section). Which I have configured as follows:
Configure the alarm threshold settings
Alarm If Redundancy Under: n+0
Alarm If Load Over: Never kVA
Alarm If Runtime Under: 0 Minutes
Yet it still beeps whenever the UPS is on battery. Is there another setting? Can I silence this beast?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:24 AM . Last Modified: 2024-03-19 01:03 AM
i think it might be under the display -> beeper menu?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:24 AM . Last Modified: 2024-03-19 01:03 AM
I didn't realize the were settings only accessible form the display (I only configured via the web interface so far). Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:24 AM . Last Modified: 2024-03-19 01:03 AM
ohhh yup. cant configure that remotely
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:24 AM . Last Modified: 2024-03-19 01:03 AM
i think it might be under the display -> beeper menu?