Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
You can subscribe to this forum after you log in or create your free account..
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
Posted: 2021-06-28 05:11 AM
This was originally posted on APC forums on 11/11/2016
Hello, i can not start it if it is not plugged in. It is a Smart ups 1000 SUA. Until two months ago I had no problem. There is a way to reset to factory settings? When I changed the batteries I had a problem and i solved it with APCFIX(Battery Const.) I thought it was the battery and I changed. Even after changing the batteries cold start don't work.
Posted: 2021-06-28 05:11 AM
This was originally posted on APC forums on 11/15/2016
I solved the problem with Hyperterminal. Connect apc com cable, make a new connection in Hyperterminal and press z key. Not Z(caps look). On the window must appear CLEAR. If don't work repeat the process and press z for several times.
Posted: 2021-06-28 05:11 AM
This reply was originally posted by Bill on APC forums on 11/14/2016
Hi,
To reset the UPS
1) Turn off and unplug UPS from wall
2) Press and hold the OFF button again
3) You may see a quick flash of the LED's and you should hear an audible "click" from the UPS.
4) Plug UPS back into the wall and turn UPS back on
Posted: 2021-06-28 05:11 AM
This was originally posted on APC forums on 11/14/2016
Now after 10 20 times start. The problem is starting with overload light.
Posted: 2021-06-28 05:11 AM
This was originally posted on APC forums on 11/15/2016
I solved the problem with Hyperterminal. Connect apc com cable, make a new connection in Hyperterminal and press z key. Not Z(caps look). On the window must appear CLEAR. If don't work repeat the process and press z for several times.
Posted: 2021-06-28 05:11 AM
This was originally posted on APC forums on 4/11/2018
I have same error with apc sua3000rmi2u but z clear still cannot cold start. Although plugging it run normal. How can i solve?
User | Count |
---|---|
4836 | |
190 | |
111 | |
108 | |
67 | |
63 |
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.