APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:26 AM . Last Modified: 2 weeks ago
Hi there!
My first APC in a very long time also fist post in this forum, so my apology in advance, if this has been answered.
I recently bought a SMT1000RMI2UC and AP9630 to go in it. They both seem to be working file as their own but I cannot talk to the UPS from the client using apcupsd. I tried with pfSense and also a from a vanilla Ubuntu (18.04) but all resulted in the same thing.
So, this is my apcupsd.conf:
The service seems start okay but within a min or so, I get the message saying communication has been lost:
and the STATUS is always COMMLOST:
Thing to note that I'm using PCNET over Ethernet (as opposed to directly USB-attached). All the firmware are updated to it's latest:
Does anyone know what am I doing wrong? Any help will be greatly appreciated. Doesn't look like the card or UPS is faulty, right?
-S
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:26 AM . Last Modified: 2 weeks ago
Hi Gavan, thanks for your reply!
I figured out last night why it was not working. I think, how it's supposed to work not really documented clearly, at least I didn't find out....... but scattered around in this forum discussions and the some of the docs. First of all, for the PCNET type, it uses pass/auth phrase instead of password and that needs to defined in the NMC web-gui, which is placed in rather odd-place: under Configuration > Shutdown
re. https://www.se.com/uk/en/faqs/FA159659/
That user (e.g. netman, which I setup as a network-only user) must be created first. PCNS uses both the password & pass-phrase for that user and APCUPSD uses only the pass-phrase. After that both started working.
-S
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:26 AM . Last Modified: 2 weeks ago
Hi Santanu,
APCUPSD is a third party software so I can't help you with that, but what I would recommend is that you look at Powerchute Network Edition. PCNS supports Ubuntu and may other types of Linux, you can download it from the link below:
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:26 AM . Last Modified: 2 weeks ago
Hi Gavan, thanks for your reply!
I figured out last night why it was not working. I think, how it's supposed to work not really documented clearly, at least I didn't find out....... but scattered around in this forum discussions and the some of the docs. First of all, for the PCNET type, it uses pass/auth phrase instead of password and that needs to defined in the NMC web-gui, which is placed in rather odd-place: under Configuration > Shutdown
re. https://www.se.com/uk/en/faqs/FA159659/
That user (e.g. netman, which I setup as a network-only user) must be created first. PCNS uses both the password & pass-phrase for that user and APCUPSD uses only the pass-phrase. After that both started working.
-S
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.