Hi,
I have install PCNS 4.0 as an virtuall appliance, and are trying to connect it to an Smart-UPS SRT 6000.
But I cannot get it to accept username and password when registrering PCNS to the NMC.
I have verified several times that the username and autentication passphrase matches, but I only get "Security information for xxxx is incorrect. Please check that the PowerChute User Name and Authentication Phrase match the Network Management Card."
In the log on the UPS i cannot se any failed attempt when trying to connect from PCNS, I have also tried giving false credentials manually through my browser and then a failed login attempt pops up.
The log file on the appliance gives the following error when I try to connect from PCNS setup "ERROR pool-1-thread-34 com.apcc.m11.components.StdPowerSource.NMCComs - java.lang.SecurityException: Control set could not be authenticated"
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:42 AM . Last Modified: 2024-02-29 11:05 PM
Reset the authentication phrase to the default admin user phrase and reboot the NMC then enter that phrase in PCNS.
Note:
The authentication phrase must be at least 15, but no more than 32 characters. You must use ASCII characters A-Z, a-z, 0-9
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:42 AM . Last Modified: 2024-02-29 11:05 PM
Reset the authentication phrase to the default admin user phrase and reboot the NMC then enter that phrase in PCNS.
Note:
The authentication phrase must be at least 15, but no more than 32 characters. You must use ASCII characters A-Z, a-z, 0-9