APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:44 AM . Last Modified: 2024-03-05 12:23 AM
Hello, I have the following problem:
I have installed PCNS on a Windows 2012 R2 server.
During the configuration I provide all neccesery (and double checked) info to connect two APC's but I keep gettting this errors:
192.168.1.228
Security information for http://192.168.1.228:80 is incorrect.
Please check that the PowerChute User Name and Authentication Phrase match the Network Management Card.
192.168.1.229
Security information for http://192.168.1.229:80 is incorrect.
Please check that the PowerChute User Name and Authentication Phrase match the Network Management Card.
Login names are default; apc/apc and I changed the Authentication Phrase to a new one with 16 caracters both numbers and capitals
I also tried it with the default Authentication Phrase: admin user phrase, still no luck
Any ideas to get this stuff working??
Peter
User Name : apc
Password : ***
American Power Conversion Network Management Card AOS v5.1.7
(c) Copyright 2010 All Rights Reserved Smart-UPS & Matrix-UPS APP v5.1.7
-------------------------------------------------------------------------------
Name : xxx Date : 2014-05-20
Contact : xxx Time : 13:56:36
Location : xxx User : Administrator
Up Time : 195 Days 23 Hours 5 Minutes Stat : P+ N+ A+
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:45 AM . Last Modified: 2024-03-05 12:23 AM
Peter,
You should reset the NMCs to defaults with the exception of TCP/IP info and then reboot the cards (see screenshot below). This will reset the user name, password, and authentication phrase. Once the NMCs reboot restart the PCNS service on the Windows system. When PCNS restarts it should connect to the NMCs.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:45 AM . Last Modified: 2024-03-05 12:23 AM
Peter,
You should reset the NMCs to defaults with the exception of TCP/IP info and then reboot the cards (see screenshot below). This will reset the user name, password, and authentication phrase. Once the NMCs reboot restart the PCNS service on the Windows system. When PCNS restarts it should connect to the NMCs.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:45 AM . Last Modified: 2024-03-05 12:23 AM
Thnx!! This worked
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.