In particular, I want to add a 3 battery XR Frame from the Symmetra, SYBFXR3RM cabinet specifically.
It appears that physically I can connect it.
But would it work?
-D
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:39 AM . Last Modified: 1 week ago
this has not been tested or supported and you would definitely not get any battery management on the system since there would be no way for the UPS to determine when there is a failed battery.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:39 AM . Last Modified: 1 week ago
Hi Dan,
The Symmetra BP cannot be used on the SU5000RMXLT5U. Though it looks like it can be attached, the battery charging power of the UPS is not enough to charge them and might cause failure on the UPS.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:39 AM . Last Modified: 1 week ago
this has not been tested or supported and you would definitely not get any battery management on the system since there would be no way for the UPS to determine when there is a failed battery.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.