APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:47 PM . Last Modified: 2024-03-14 11:37 PM
I am trying to do some troubleshooting on a SU2200XLNET ups that doesn't have any batteries with it. I wanted to check and make sure it was okay to put batteries from either a SUA1000XL or SUA24XLBP into the SU2200XLNET before I messed something up. Thanks!!!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:47 PM . Last Modified: 2024-03-14 11:37 PM
This would not be supported and the UPS would fail to start up properly. The batteries for the SUA1000XL/battery pack systems differ greatly from the older SU systems, not to mention the size differences (physical/battery capacity/type) of the SUA1000xl/su2200xlnet units.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:47 PM . Last Modified: 2024-03-14 11:37 PM
According to APC's website the replacement battery pack for the SU2200XLNET is the RBC#11 and the replacement battery pack for the SUA24XLBP is also the RBC#11. I have already switched the batteries from the SUA24XLBP into the SU2200XLNET and it turned on perfectly. It is charging the batteries right now and will switch to batteries if I unplug the main power for the UPS and switch back once I plug the main power back in. Currently there is no load on the UPS but once the batteries are charged I am going to plug some things into it and give it some load to work with.
These are the results I got after using APC's battery replacement selector -
http://www.apc.com/tools/upgrade_selector/?CFID=18252204&CFTOKEN=32635653
SUA24XLBP -
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=RBC11&fnl=3944,2&fnl_basket=3944,3c
SU2200XLNET -
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=RBC11&fnl=3944,2&fnl_basket=3944,3c
Does this sound like it should still work???
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:47 PM . Last Modified: 2024-03-14 11:37 PM
I'm rather embarrassed about making a mix up like that, but:
The RBC11 will work just fine with the SU2200XLNET. You should have no problems with that configuration. I had the RBC for the SUA unit itself stuck in my head when answering. Sorry for any confusion that was caused.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:47 PM . Last Modified: 2024-03-14 11:37 PM
No problem, I just wanted to make sure it would work. Thanks for the help!!!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:47 PM . Last Modified: 2024-03-14 11:37 PM
This would not be supported and the UPS would fail to start up properly. The batteries for the SUA1000XL/battery pack systems differ greatly from the older SU systems, not to mention the size differences (physical/battery capacity/type) of the SUA1000xl/su2200xlnet units.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.