Can I put my SUA1000XL batteries into a SUA2200XLNET???

This was originally posted on APC forums on 4/16/2009


I am trying to do some troubleshooting on a SU2200XLNET ups that doesn't have any batteries with it. I wanted to check and make sure it was okay to put batteries from either a SUA1000XL or SUA24XLBP into the SU2200XLNET before I messed something up. Thanks!!!


Accepted Solutions
Erasmus_apc
Sisko
Sisko
0 Likes
0
146

Re: Can I put my SUA1000XL batteries into a SUA2200XLNET???

This was originally posted on APC forums on 4/16/2009


This would not be supported and the UPS would fail to start up properly. The batteries for the SUA1000XL/battery pack systems differ greatly from the older SU systems, not to mention the size differences (physical/battery capacity/type) of the SUA1000xl/su2200xlnet units.

See Answer In Context

4 Replies 4
logoldman_apc
Ensign
Ensign
0 Likes
0
146

Re: Can I put my SUA1000XL batteries into a SUA2200XLNET???

This was originally posted on APC forums on 4/16/2009


According to APC's website the replacement battery pack for the SU2200XLNET is the RBC#11 and the replacement battery pack for the SUA24XLBP is also the RBC#11. I have already switched the batteries from the SUA24XLBP into the SU2200XLNET and it turned on perfectly. It is charging the batteries right now and will switch to batteries if I unplug the main power for the UPS and switch back once I plug the main power back in. Currently there is no load on the UPS but once the batteries are charged I am going to plug some things into it and give it some load to work with.

These are the results I got after using APC's battery replacement selector -
http://www.apc.com/tools/upgrade_selector/?CFID=18252204&CFTOKEN=32635653

SUA24XLBP -
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=RBC11&fnl=3944,2&fnl_basket=3944,3c

SU2200XLNET -
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=RBC11&fnl=3944,2&fnl_basket=3944,3c

Does this sound like it should still work???

Erasmus_apc
Sisko
Sisko
0 Likes
0
145

Re: Can I put my SUA1000XL batteries into a SUA2200XLNET???

This was originally posted on APC forums on 4/17/2009


I'm rather embarrassed about making a mix up like that, but:

The RBC11 will work just fine with the SU2200XLNET. You should have no problems with that configuration. I had the RBC for the SUA unit itself stuck in my head when answering. Sorry for any confusion that was caused.

logoldman_apc
Ensign
Ensign
0 Likes
0
145

Re: Can I put my SUA1000XL batteries into a SUA2200XLNET???

This was originally posted on APC forums on 4/17/2009


No problem, I just wanted to make sure it would work. Thanks for the help!!!

Erasmus_apc
Sisko
Sisko
0 Likes
0
147

Re: Can I put my SUA1000XL batteries into a SUA2200XLNET???

This was originally posted on APC forums on 4/16/2009


This would not be supported and the UPS would fail to start up properly. The batteries for the SUA1000XL/battery pack systems differ greatly from the older SU systems, not to mention the size differences (physical/battery capacity/type) of the SUA1000xl/su2200xlnet units.