Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79162members
343647posts

Can I put my SUA1000XL batteries into a SUA2200XLNET???

Solved
logoldman_apc
Ensign
Ensign
0 Likes
4
139

Can I put my SUA1000XL batteries into a SUA2200XLNET???

This was originally posted on APC forums on 4/16/2009


I am trying to do some troubleshooting on a SU2200XLNET ups that doesn't have any batteries with it. I wanted to check and make sure it was okay to put batteries from either a SUA1000XL or SUA24XLBP into the SU2200XLNET before I messed something up. Thanks!!!


Accepted Solutions
Erasmus_apc
Sisko
Sisko
0 Likes
0
141

Re: Can I put my SUA1000XL batteries into a SUA2200XLNET???

This was originally posted on APC forums on 4/16/2009


This would not be supported and the UPS would fail to start up properly. The batteries for the SUA1000XL/battery pack systems differ greatly from the older SU systems, not to mention the size differences (physical/battery capacity/type) of the SUA1000xl/su2200xlnet units.

See Answer In Context

4 Replies 4
logoldman_apc
Ensign
Ensign
0 Likes
0
141

Re: Can I put my SUA1000XL batteries into a SUA2200XLNET???

This was originally posted on APC forums on 4/16/2009


According to APC's website the replacement battery pack for the SU2200XLNET is the RBC#11 and the replacement battery pack for the SUA24XLBP is also the RBC#11. I have already switched the batteries from the SUA24XLBP into the SU2200XLNET and it turned on perfectly. It is charging the batteries right now and will switch to batteries if I unplug the main power for the UPS and switch back once I plug the main power back in. Currently there is no load on the UPS but once the batteries are charged I am going to plug some things into it and give it some load to work with.

These are the results I got after using APC's battery replacement selector -
http://www.apc.com/tools/upgrade_selector/?CFID=18252204&CFTOKEN=32635653

SUA24XLBP -
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=RBC11&fnl=3944,2&fnl_basket=3944,3c

SU2200XLNET -
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=RBC11&fnl=3944,2&fnl_basket=3944,3c

Does this sound like it should still work???

Erasmus_apc
Sisko
Sisko
0 Likes
0
142

Re: Can I put my SUA1000XL batteries into a SUA2200XLNET???

This was originally posted on APC forums on 4/17/2009


I'm rather embarrassed about making a mix up like that, but:

The RBC11 will work just fine with the SU2200XLNET. You should have no problems with that configuration. I had the RBC for the SUA unit itself stuck in my head when answering. Sorry for any confusion that was caused.

logoldman_apc
Ensign
Ensign
0 Likes
0
142

Re: Can I put my SUA1000XL batteries into a SUA2200XLNET???

This was originally posted on APC forums on 4/17/2009


No problem, I just wanted to make sure it would work. Thanks for the help!!!

Erasmus_apc
Sisko
Sisko
0 Likes
0
142

Re: Can I put my SUA1000XL batteries into a SUA2200XLNET???

This was originally posted on APC forums on 4/16/2009


This would not be supported and the UPS would fail to start up properly. The batteries for the SUA1000XL/battery pack systems differ greatly from the older SU systems, not to mention the size differences (physical/battery capacity/type) of the SUA1000xl/su2200xlnet units.