Hi,
We've got ten servers and four SMART 3000 UPS's. We've recently bought four network management cards for them.
We would like each server to have redundant power supplies, so the server's two PSU's are powered by a different UPS.
Which software would be best with this configuration? PowerChute Business Edition or PowerChute Network Shutdown?
I initially thought PCNS, but does this allow registration of TWO network cards (i.e. two UPS's) so it will only trigger shutdown if BOTH send critical signals?
Cheers
Ian
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:21 AM . Last Modified: 2024-03-13 05:42 AM
Thank you very much for your quick and thorough reply! It is very much appreciated.
Merry xmas! 🙂
Ian
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:21 AM . Last Modified: 2024-03-13 05:42 AM
Thank you very much for your quick and thorough reply! It is very much appreciated.
Merry xmas! 🙂
Ian
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:21 AM . Last Modified: 2024-03-13 05:42 AM
yes, you can do this. if you have network management cards, you should be using PCNS. there is an option in PCNS to do a "multiple UPS scenario" and then you can provide it two IPs. it will shutdown when both UPSs have sent a low battery signal.
[here is an article that also has more info on a multiple UPS scenario|http://nam-en.apc.com/app/answers/detail/a_id/3143/]
hope that helps.
P.S. - in general, it is advised to use either PCBE or PCNS.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:21 AM . Last Modified: 2024-03-13 05:42 AM
Thanks for your quick reply. I've got another quick question if that's ok.
So what software would you recommend for this scenario? Can PCBE do the same thing: graceful shutdown of servers connected to two UPS's, when both UPS's send a critical signal?
I'm confused about the whole Server/Agent/Console thing. I know I install 'Server' on the server that's directly connected to the UPS, but isnt this via USB or serial? And doesnt that remove the need for a network card?
I was under the impression that the only way we could have graceful shutdown of a server that is powered by two UPS was with network cards and PCNS. And that it was not possible with PCBE. Is that right?
I like PCBE because of the Console - a central hub to manage it all. Does PCNS have such a thing?
Thanks for your help.
Cheers
Ian
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:21 AM . Last Modified: 2024-03-13 05:42 AM
sure, you can ask questions 🙂
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:21 AM . Last Modified: 2024-03-13 05:42 AM
no problem. you too