Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79125members
343513posts

Breaker reset on modular power unit

Solved
BillP
Administrator Administrator
Administrator
0 Likes
1
124

Breaker reset on modular power unit

This question was originally posted by James on APC forums on 3/8/2015


I have breakers that have 3 poles connected with 'handle ties'.  From what i gathered, this is safety mechanism for 3 wires sharing same neutral. No issue with that, but when a single leg trips due to device issue that backfeeds to the breaker, my question is, can I remove the handle tie to reset only that leg?  It appears the handle tie is removable and used for codes where needed.  I dont think it would be any code violation to remove it to reset the breaker, but I can not find any information on this.  Has anyone here had this experience?  I really do not want to reset all 3 phases as other devices do not need the added disruption of power off, then on.

this is on pdpm277 with breaker pdm3520, 3 phase, 5 wire breaker.


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
124

Re: Breaker reset on modular power unit

This reply was originally posted by Angela on APC forums on 3/9/2015


Hello,

I checked with our 3 phase power team for help on this. Here is what they told me:

The installation of the handle ties are based on the load type (single or 3 phase & voltage).
This is regulated by the NEC.
IE: If the load is 120V single phase, then no handle tie is required since only a single pole breaker is needed for this type of load. If load is 208V or 277V single phase, then a 2 pole breaker is needed and therefore on a 3 pole breaker module, you would need a handle tie on 2 of the 3 breakers. If load is 208V 3 phase, then a handle tie would be needed across all 3 breakers.
The NEC Code requires that a circuit breaker providing power to any given load needs to open all current carrying conductors for that load at the same time during a fault.
So, if you are resetting a single phase load ( 120V or 277 ) then yes, you can reset the individual breaker, otherwise, no.

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
125

Re: Breaker reset on modular power unit

This reply was originally posted by Angela on APC forums on 3/9/2015


Hello,

I checked with our 3 phase power team for help on this. Here is what they told me:

The installation of the handle ties are based on the load type (single or 3 phase & voltage).
This is regulated by the NEC.
IE: If the load is 120V single phase, then no handle tie is required since only a single pole breaker is needed for this type of load. If load is 208V or 277V single phase, then a 2 pole breaker is needed and therefore on a 3 pole breaker module, you would need a handle tie on 2 of the 3 breakers. If load is 208V 3 phase, then a handle tie would be needed across all 3 breakers.
The NEC Code requires that a circuit breaker providing power to any given load needs to open all current carrying conductors for that load at the same time during a fault.
So, if you are resetting a single phase load ( 120V or 277 ) then yes, you can reset the individual breaker, otherwise, no.