APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:21 AM . Last Modified: 3 weeks ago
Full battery, only one server behind and a battery runtime less than 1 minute?
This UPS is a half year old...
What's wrong here?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:21 AM . Last Modified: 3 weeks ago
Hello,
Try resetting the UPS.
1: Disconnect any attached load.
2: Unplug the UPS from the wall socket.
3: Disconnect the UPS' internal battery.
4: Push and hold the "On" button on the UPS for 5 seconds
5: Reconnect internal battery.
6: Plug UPS in to known good power source.
7: Turn UPS on.
If the reset does not resolve the issue please contact local technical support. Since the UPS is only 6 months old it is under warranty and may need to be replaced.
Local support contact information will be found at this link.
https://www.apc.com/us/en/support/contact-us/index.jsp
You may need to change the region in the upper left of the contact us web page.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:21 AM . Last Modified: 3 weeks ago
Hello,
Try resetting the UPS.
1: Disconnect any attached load.
2: Unplug the UPS from the wall socket.
3: Disconnect the UPS' internal battery.
4: Push and hold the "On" button on the UPS for 5 seconds
5: Reconnect internal battery.
6: Plug UPS in to known good power source.
7: Turn UPS on.
If the reset does not resolve the issue please contact local technical support. Since the UPS is only 6 months old it is under warranty and may need to be replaced.
Local support contact information will be found at this link.
https://www.apc.com/us/en/support/contact-us/index.jsp
You may need to change the region in the upper left of the contact us web page.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.