Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79173members
343669posts

Battery for APC SmartUPS 2200

Solved
BillP
Administrator Administrator
Administrator
0 Likes
1
152

Battery for APC SmartUPS 2200

This question was originally posted by alvaro on APC forums on 1/14/2016


I need to replace the battery of my UPS. Do I need to turn off the UPS? I have connected my server to that UPS and I would prefer not to turn it off.

Any suggestion what do I need to do? Urgent matter.

 

Thanks,


Accepted Solutions
mitsmith_apc
Lt. Commander
Lt. Commander
0 Likes
0
152

Re: Battery for APC SmartUPS 2200

This was originally posted on APC forums on 1/14/2016


Hi Alvaro,

You do not need to turn the unit off to replace the battery. They are hot swappable for the smart-ups 2200.

Regards,

Mike 

See Answer In Context

1 Reply 1
mitsmith_apc
Lt. Commander
Lt. Commander
0 Likes
0
153

Re: Battery for APC SmartUPS 2200

This was originally posted on APC forums on 1/14/2016


Hi Alvaro,

You do not need to turn the unit off to replace the battery. They are hot swappable for the smart-ups 2200.

Regards,

Mike