Battery for APC SmartUPS 2200

This question was originally posted by alvaro on APC forums on 1/14/2016


I need to replace the battery of my UPS. Do I need to turn off the UPS? I have connected my server to that UPS and I would prefer not to turn it off.

Any suggestion what do I need to do? Urgent matter.

 

Thanks,


Accepted Solutions
mitsmith_apc
Lt. Commander
Lt. Commander
0 Likes
0
160

Re: Battery for APC SmartUPS 2200

This was originally posted on APC forums on 1/14/2016


Hi Alvaro,

You do not need to turn the unit off to replace the battery. They are hot swappable for the smart-ups 2200.

Regards,

Mike 