Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79278members
343949posts

Bank 1 16A output fails in ATS 7724

Solved
jarguelles_apc
Crewman
Crewman
0 Likes
1
107

Bank 1 16A output fails in ATS 7724

This was originally posted on APC forums on 7/11/2013



Good morning.

Recently I bought a rack automatic transfer switch ATS 7724. We have connected both UPS to both inputs: A and B.

I have only voltage in the outputs of the BANK 1 16A, but not the BANK 2.

Could someone help me?

Thank you very much.


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
108

Re: Bank 1 16A output fails in ATS 7724

This reply was originally posted by Angela on APC forums on 7/11/2013


First thing to do is check the status of the breaker for Bank 2.

Please review this document below and try full tripping the breaker and resetting it. Or let us know if the breaker is damaged.

http://www.apcmedia.com/salestools/ASTE-6Z6K8Q/ASTE-6Z6K8Q_R0_EN.pdf

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
109

Re: Bank 1 16A output fails in ATS 7724

This reply was originally posted by Angela on APC forums on 7/11/2013


First thing to do is check the status of the breaker for Bank 2.

Please review this document below and try full tripping the breaker and resetting it. Or let us know if the breaker is damaged.

http://www.apcmedia.com/salestools/ASTE-6Z6K8Q/ASTE-6Z6K8Q_R0_EN.pdf