Scenario...
APC750 (SMT750RMI2U) is located in a fairly remote location.
We recently lost primary power to the space and the batteries ran dead.
Once the normal primary power was restored, the APC 750 had to be "manually" turned back on.
This is quite inconvenient due to the driving distance from the main office.
Is there a setting in this APC device that will automatically initialize the device upon restoration
of regular primary power?
Thanks in advance.
Kevin
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:09 AM . Last Modified: 2 weeks ago
If the UPS turns off due to a low battery (with no intervention from software via USB or serial or a UPS Network Management Card), then it should turn back on automatically when AC power is restored.
Let's start here - do you have PowerChute Business Edition in use via serial/USB or is there a UPS Network Management Card installed in this UPS?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:09 AM . Last Modified: 2 weeks ago
If the UPS turns off due to a low battery (with no intervention from software via USB or serial or a UPS Network Management Card), then it should turn back on automatically when AC power is restored.
Let's start here - do you have PowerChute Business Edition in use via serial/USB or is there a UPS Network Management Card installed in this UPS?