Application is not compatible with the AOS.' due to the 'Status : P+ N+ A!' for acrc103

Solved
omni_apc
Cadet
0 Likes
4
155

Application is not compatible with the AOS.' due to the 'Status : P+ N+ A!' for acrc103

This was originally posted on APC forums on 8/9/2013


Hi

In telnet i have the error - Indicates that the application is not compatible with the AOS.' due to the 'Status : P+ N+ A!' and i can't access it on the web, only telnet, and the display of the unit it's blank, and no butons function.

I tried to uprgade the firmware, but the problem doesn't dissapear. The same if a made a downgrade of the firmware.

the unit is working, but because of this i suspect that one of the other 8 units from the group have alarm - lost group communication. If i cleare the alarm it appears after 15 sec, and if i shutdown the unit from the main supply, the alarm appears to another unit.

Pls help me to find an AOS that is compatible with the application.

Thanks in advanced.


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
155

Re: Application is not compatible with the AOS.' due to the 'Status : P+ N+ A!' for acrc103

This reply was originally posted by L2SupportServices-Cooling on APC forums on 8/9/2013


Hello.

     The ACRC103 unit needs the application section of the firmware loaded for it to work right. You will see P+N+A+ when it is loaded properly.I have included a link to our website, where you can download the 373 firmware which is the newest version. I have also included a link to our knowledge base. If you search for "FA156047", this will pull up a document that will walk you through the upgrade process (use the NMC 1 instructions). If you choose to use the serial (XModem) method there are 2 changes to the document. First use a null modem cable and second, it is 9600 bits per second not 2400.

     For the group communication alarm, if the unit that does not have the firmware loaded on it is in the group, then that is the cause of the group comm loss alarms. Getting the firmware on the unit so it is seen by the group again will cause the group comm loss alarms to clear. If you need any help upgrading the firmware you can call into our tech support lines (North America 888-695-6500 opt 2) and we can help you through the firmware upgrade.

Thank you

FAQ

InRow RC, 300mm, Chilled Water, 100-120V, 50/60 Hz - Download Software and Firmware | APC

See Answer In Context

4 Replies 4
BillP
Administrator Administrator
Administrator
0 Likes
0
156

Re: Application is not compatible with the AOS.' due to the 'Status : P+ N+ A!' for acrc103

This reply was originally posted by L2SupportServices-Cooling on APC forums on 8/9/2013


Hello.

     The ACRC103 unit needs the application section of the firmware loaded for it to work right. You will see P+N+A+ when it is loaded properly.I have included a link to our website, where you can download the 373 firmware which is the newest version. I have also included a link to our knowledge base. If you search for "FA156047", this will pull up a document that will walk you through the upgrade process (use the NMC 1 instructions). If you choose to use the serial (XModem) method there are 2 changes to the document. First use a null modem cable and second, it is 9600 bits per second not 2400.

     For the group communication alarm, if the unit that does not have the firmware loaded on it is in the group, then that is the cause of the group comm loss alarms. Getting the firmware on the unit so it is seen by the group again will cause the group comm loss alarms to clear. If you need any help upgrading the firmware you can call into our tech support lines (North America 888-695-6500 opt 2) and we can help you through the firmware upgrade.

Thank you

FAQ

InRow RC, 300mm, Chilled Water, 100-120V, 50/60 Hz - Download Software and Firmware | APC

BillP
Administrator Administrator
Administrator
0 Likes
0
155

Re: Application is not compatible with the AOS.' due to the 'Status : P+ N+ A!' for acrc103

This reply was originally posted by Angela on APC forums on 8/9/2013


Since it appears your in the EMEA region, you can use http://www.apc.com/support/contact/index.cfm to contact technical support for your region if the steps above do not work.

omni_apc
Cadet
0 Likes
0
155

Re: Application is not compatible with the AOS.' due to the 'Status : P+ N+ A!' for acrc103

This was originally posted on APC forums on 8/9/2013


Thank you for the fast answer, i did what you tell me, but after downloading the 3.7.3 firmware application and run it, i have the same status and the same problem.

BillP
Administrator Administrator
Administrator
0 Likes
0
155

Re: Application is not compatible with the AOS.' due to the 'Status : P+ N+ A!' for acrc103

This reply was originally posted by L2SupportServices-Cooling on APC forums on 8/9/2013


Hello.

If this is the case then the application is not loading properly. If you are just using the executable file to try and upload the firmware, try the ftp or XModem.

Thank you