Posted: 2021-06-29 12:41 AM
This was originally posted on APC forums on 7/19/2010
Just hooked up a Smart UPS 1000, connected the battery and plugged it in. All four lights in the front are on, and staying on, not flashing. The LCD screen is blank. No power to the outlets in the back. Did I get a broken unit? Or do I need to do something else to get this going?
Thanks,
Chris
Posted: 2021-06-29 12:41 AM
This was originally posted on APC forums on 7/19/2010
Just hooked up a Smart UPS 1000, connected the battery and plugged it in. All four lights in the front are on, and staying on, not flashing. The LCD screen is blank. No power to the outlets in the back. Did I get a broken unit? Or do I need to do something else to get this going?
Thanks,
Chris
Posted: 2021-06-29 12:41 AM
This was originally posted on APC forums on 7/20/2010
Thank you, that was the problem. All fixed now!
Posted: 2021-06-29 12:41 AM
This reply was originally posted by Jonathan on APC forums on 7/20/2010
We're glad to help you out Chris. Have a great day!
Posted: 2021-06-29 12:41 AM
This was originally posted on APC forums on 7/19/2010
Just hooked up a Smart UPS 1000, connected the battery and plugged it in. All four lights in the front are on, and staying on, not flashing. The LCD screen is blank. No power to the outlets in the back. Did I get a broken unit? Or do I need to do something else to get this going?
Thanks,
Chris