APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:07 AM . Last Modified: 2024-03-12 07:22 AM
Schneider Electric Network Management Card AOS v6.8.8
(c) Copyright 2020 All Rights Reserved
https: : Enabled https: : Enabled
FTP : Enabled Telnet : Disabled
SSH/SCP : Enabled
ssh to network card works
https:, https: works, but shows error
web page error
The Application Was Not Able to Load | ||||||
|
************* ssh working ***********
ssh dialog
apc>about
E000: Success
Hardware Factory
---------------
Model Number: AP9630
Serial Number: ZA1317004817
Hardware Revision: 05
Manufacture Date: 04/23/2013
MAC Address: 00 C0 B7 B2 C5 44
Management Uptime: 0 Days 1 Hour 22 Minutes
Application Module
---------------
Name: aos
Version: v6.8.8
Date: Apr 28 2020
Time: 17:21:52
APC OS(AOS)
---------------
Name: aos
Version: v6.8.8
Date: Apr 28 2020
Time: 17:21:52
APC Boot Monitor
---------------
Name: bootmon
Version: v1.0.2
Date: Jan 21 2010
Time: 13:35:57
apc>
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:07 AM . Last Modified: 2024-03-08 03:13 AM
Hi John,
I presume its a Smart-UPS you are trying to update?
Can you reset the card to factory default, apply the update again and then reset the card again.
Also download a new copy of the update:
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:07 AM . Last Modified: 2024-03-08 03:13 AM
Hi John,
I presume its a Smart-UPS you are trying to update?
Can you reset the card to factory default, apply the update again and then reset the card again.
Also download a new copy of the update:
-Gavan