Hi,
After AOS Firmware Upgrade (3.5.8/3.6.1) on a NMC9617 i can not do WebLogin only Telnet:
Error: The application was not able to load.
You are attempting to access an APC device.
There was a problem loading the application. Please login to the device via telnet for more details.
Can you help me? Thanks.
Kind regards
Joerg
Message was edited by: joerg.schmidtke@cuc.de
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:56 PM . Last Modified: Thursday
hi joerg,
you should be able to remedy this problem by reflashing the firmware via manual FTP. use the same bin files that you should have extracted (AOS 3.6.1 and APP 3.5.8) and follow [these instructions|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=8515].
that should fix it. let us know how you make out.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:56 PM . Last Modified: Thursday
hi joerg,
you should be able to remedy this problem by reflashing the firmware via manual FTP. use the same bin files that you should have extracted (AOS 3.6.1 and APP 3.5.8) and follow [these instructions|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=8515].
that should fix it. let us know how you make out.