Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
80721members
346686posts

APCPBEAgent apc pbe agent fail Error: 6, SetServiceStatus

Solved
wantedsanzo_apc
Crewman
Crewman
0 Likes
2
121

APCPBEAgent apc pbe agent fail Error: 6, SetServiceStatus

This was originally posted on APC forums on 2/24/2015


I am using PBE BUSNESS in windows 8.1
Recently, there was always apc pbe agent service fail to server
Windows event detector review found

- System
- Provider
[ Name] APCPBEAgent
- EventID 0
[ Qualifiers] 33023
Level 2
Task 0
Keywords 0x80000000000000
- TimeCreated
[ SystemTime] 2015-02-22T10:29:12.000000000Z
EventRecordID 64096
Channel Application
Computer wesley-npc
Security
- EventData
Error: 6, SetServiceStatus


Accepted Solutions
wantedsanzo_apc
Crewman
Crewman
0 Likes
0
121

Re: APCPBEAgent apc pbe agent fail Error: 6, SetServiceStatus

This was originally posted on APC forums on 2/24/2015


Thanks! I use windows 8.1 64bit.

See Answer In Context

2 Replies 2
BillP
Administrator Administrator
Administrator
0 Likes
0
121

Re: APCPBEAgent apc pbe agent fail Error: 6, SetServiceStatus

This reply was originally posted by Bill on APC forums on 2/24/2015


Hi,

You should uninstall PowerChute and then reinstall. The error could be caused by memory handling. Also, what version of Windows 8.1 and is the system 32 or 64 bit?

wantedsanzo_apc
Crewman
Crewman
0 Likes
0
122

Re: APCPBEAgent apc pbe agent fail Error: 6, SetServiceStatus

This was originally posted on APC forums on 2/24/2015


Thanks! I use windows 8.1 64bit.