Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79378members
344113posts

APC Smart-UPS RT 5000 RS232 and usb cable

Solved
aregmartirosyan_apc
Ensign
Ensign
0 Likes
8
948

APC Smart-UPS RT 5000 RS232 and usb cable

This was originally posted on APC forums on 4/11/2016


Please can you tell me the correct models of USB and com cables for APC Smart-UPS RT 5000, I have 940-0127b usb-RJ50 cable but I dont now is it right cable for this UPS. Thank you


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
949

Re: APC Smart-UPS RT 5000 RS232 and usb cable

This reply was originally posted by Bill on APC forums on 4/11/2016


Hi,

What is the exact model and serial number of the Smart-UPS?

You will find the information on the bar code sticker on back of the UPS.

See Answer In Context

Attachments
BillP
Administrator Administrator
Administrator
0 Likes
0
949

Re: APC Smart-UPS RT 5000 RS232 and usb cable

This reply was originally posted by Bill on APC forums on 4/11/2016


Hi,

The cable for that UPS is part number 940-0625. It is 9 pin serial to RJ50. 

See Answer In Context

Attachments
aregmartirosyan_apc
Ensign
Ensign
0 Likes
0
949

Re: APC Smart-UPS RT 5000 RS232 and usb cable

This was originally posted on APC forums on 4/12/2016


Thank you very much and what part number is USB cable, will my 940-0127b connect with him for monitoring. I fear, I will smash the UPS if I connect with this cable.

See Answer In Context

BillP
Administrator Administrator
Administrator
0 Likes
0
949

Re: APC Smart-UPS RT 5000 RS232 and usb cable

This reply was originally posted by Bill on APC forums on 4/12/2016


Hi,

The SURTD5000XLi does not have aUSB connection. If you would like to connect the Smart-UPS to the computer using USB you will need cable 940-0625 and a USB to serial converter. I use Plugable USB to RS-232 DB9 Serial Adapter (Prolific PL2303HX Rev D Chipset) but all serial to USB converters will work. 

See Answer In Context

aregmartirosyan_apc
Ensign
Ensign
0 Likes
0
949

Re: APC Smart-UPS RT 5000 RS232 and usb cable

This was originally posted on APC forums on 4/12/2016


Thank you Bill, very much. 

See Answer In Context

8 Replies 8
BillP
Administrator Administrator
Administrator
0 Likes
0
950

Re: APC Smart-UPS RT 5000 RS232 and usb cable

This reply was originally posted by Bill on APC forums on 4/11/2016


Hi,

What is the exact model and serial number of the Smart-UPS?

You will find the information on the bar code sticker on back of the UPS.

Attachments
aregmartirosyan_apc
Ensign
Ensign
0 Likes
0
949

Re: APC Smart-UPS RT 5000 RS232 and usb cable

This was originally posted on APC forums on 4/11/2016


Thank you Bill for response, SURTD5000XLI and serial is NS1005003519 

Attachments
BillP
Administrator Administrator
Administrator
0 Likes
0
950

Re: APC Smart-UPS RT 5000 RS232 and usb cable

This reply was originally posted by Bill on APC forums on 4/11/2016


Hi,

The cable for that UPS is part number 940-0625. It is 9 pin serial to RJ50. 

Attachments
aregmartirosyan_apc
Ensign
Ensign
0 Likes
0
950

Re: APC Smart-UPS RT 5000 RS232 and usb cable

This was originally posted on APC forums on 4/12/2016


Thank you very much and what part number is USB cable, will my 940-0127b connect with him for monitoring. I fear, I will smash the UPS if I connect with this cable.

BillP
Administrator Administrator
Administrator
0 Likes
0
950

Re: APC Smart-UPS RT 5000 RS232 and usb cable

This reply was originally posted by Bill on APC forums on 4/12/2016


Hi,

The SURTD5000XLi does not have aUSB connection. If you would like to connect the Smart-UPS to the computer using USB you will need cable 940-0625 and a USB to serial converter. I use Plugable USB to RS-232 DB9 Serial Adapter (Prolific PL2303HX Rev D Chipset) but all serial to USB converters will work. 

aregmartirosyan_apc
Ensign
Ensign
0 Likes
0
950

Re: APC Smart-UPS RT 5000 RS232 and usb cable

This was originally posted on APC forums on 4/12/2016


Thank you Bill, very much. 

aregmartirosyan_apc
Ensign
Ensign
0 Likes
0
950

Re: APC Smart-UPS RT 5000 RS232 and usb cable

This was originally posted on APC forums on 4/15/2016


Hi

I make a cable like 940-0625 with RJ-45 one side and DB9 from other from this site http://pinoutsguide.com/UPS/apc_0625_cable.shtml and connect directly to com port but powerchute agent cant cant find the ups on com port, what do yo think I make wrong?

aregmartirosyan_apc
Ensign
Ensign
0 Likes
0
950

Re: APC Smart-UPS RT 5000 RS232 and usb cable

This was originally posted on APC forums on 4/15/2016


I find the solution, I can connect to UPS only with hyperterminal then over network. Thank you