Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79298members
343972posts

APC SUA3000RM2U dead...?

Solved
glashoppah_apc
Ensign
Ensign
0 Likes
7
270

APC SUA3000RM2U dead...?

This was originally posted on APC forums on 11/6/2014


Dear Forum,

I have an APC SUA3000RM2U, which is obviously older, and has been sitting on a shelf for a few years but was pulled from a working environment.   Upon applying power to the device it exhibits absolutely no reaction whatsoever - not a single light comes on, no clicks or sounds, nothing - it's like I've plugged a rock into the power outlet.  I've checked everything I can think of, pressed all the buttons, flipped the breaker on the back, etc. to no avail.  I've also let it sit on power for 24 hours.

Should this device exhibit *some* reaction to being powered?  I don't want to buy a battery pack for it until I'm sure that will fix the problem I'm perceiving.  And if I'm missing something simple, like a fuse I didn't notice, please let me know.

Thanks in advance for any help,

J.

Tags (4)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
270

Re: APC SUA3000RM2U dead...?

This reply was originally posted by Angela on APC forums on 11/7/2014


Typically, SUA units do not require the battery to turn on. Though, if there is no DC voltage present anywhere in the system, you may need batteries to jump start it.

Was the battery in this system stored connected or disconnected? Can you measure the voltage on the existing battery pack?

See Answer In Context

7 Replies 7
BillP
Administrator Administrator
Administrator
0 Likes
0
271

Re: APC SUA3000RM2U dead...?

This reply was originally posted by Angela on APC forums on 11/7/2014


Typically, SUA units do not require the battery to turn on. Though, if there is no DC voltage present anywhere in the system, you may need batteries to jump start it.

Was the battery in this system stored connected or disconnected? Can you measure the voltage on the existing battery pack?

glashoppah_apc
Ensign
Ensign
0 Likes
0
270

Re: APC SUA3000RM2U dead...?

This was originally posted on APC forums on 11/7/2014


It was stored connected and I'm certain it is completely drained.

BillP
Administrator Administrator
Administrator
0 Likes
0
270

Re: APC SUA3000RM2U dead...?

This reply was originally posted by Angela on APC forums on 11/10/2014


From my experience, I do think it is worth a try to "jumpstart" it with new batteries, preferably if you're able to return the batteries if the UPS does happen to be the issue. I can't be sure which it is since the batteries are likely completely shot due to being stored connected and not periodically recharged.

glashoppah_apc
Ensign
Ensign
0 Likes
0
270

Re: APC SUA3000RM2U dead...?

This was originally posted on APC forums on 11/11/2014


I may try to jury-rig a 48v source and jump-start it with that first...  at $260+, the battery pack is a big risk.

glashoppah_apc
Ensign
Ensign
0 Likes
0
270

Re: APC SUA3000RM2U dead...?

This was originally posted on APC forums on 11/11/2014


OK - it worked.  I stacked 5 9v batteries and used a pair of test leads to energize the input connector from the battery pack.  Ping, on it came.  Thank you very much - it's dinging "Replace Battery" even with the old pack connected, so I'm going to order a new battery pack.

Thanks again!

glashoppah_apc
Ensign
Ensign
0 Likes
0
270

Re: APC SUA3000RM2U dead...?

This was originally posted on APC forums on 11/12/2014


Final note - new battery pack received and installed, everything working perfectly.  Thanks again.  smile

BillP
Administrator Administrator
Administrator
0 Likes
0
270

Re: APC SUA3000RM2U dead...?

This reply was originally posted by Angela on APC forums on 11/13/2014


Glad to hear. Thanks for the follow up!