APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:17 AM . Last Modified: 2024-02-29 11:22 PM
We've been running on older APC Smart-UPS devices for years and had one recently fail. I ordered and received a new APC Smart-UPS SMT2200, and noticed that the SmartSlot has changed slightly and now has tabs that pass throught the NMC faceplate. Are the APC 9617 cards we have incompatible with the newer SmartUPS systems?
Thanks,
Don
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:17 AM . Last Modified: 2024-02-29 11:21 PM
Angela/voidstar,
Thanks for the info... I've now ordered a coupld of AP9630s.
Thanks,
Don
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:17 AM . Last Modified: 2024-02-29 11:22 PM
Yes, newer UPS models such as the SMT2200 are incompatible with the AP9617 card. The AP9630 is the direct replacement. While the AP9630 will also work on older UPSes, offers additional features, and are much faster processing HTTPS and SSH connections, I would stick with using the existing AP9617 cards on them for now.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:17 AM . Last Modified: 2024-02-29 11:21 PM
Here is a link to a relatively new UPS Network Management Card compatibility chart -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA237786
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:17 AM . Last Modified: 2024-02-29 11:21 PM
Angela/voidstar,
Thanks for the info... I've now ordered a coupld of AP9630s.
Thanks,
Don
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.