APC 1500 smartups outlet groups

This question was originally posted by tgreene on APC forums on 4/18/2016


I have a APC 1500RMUNC, the outlet groups automatically turn off, an on. I have replaced the ups 3 times with brand new units. I have 150, of these ups in use at my company this is a new issue to me. Is there, a problem with the input power on the circuit that is causing this to happen ? I went through the logs, I don't see the unit switching to battery due to loss of input power. Thanks.

Tags (1)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
341

Re: APC 1500 smartups outlet groups

This reply was originally posted by tgreene on APC forums on 4/18/2016


Hi,

The issue has happened on multiple units at that location. There is not a power down schedule, or load shedding. I did check the unit for an overload condition, that doesn't appear to be the case. Since I changed the sensitivity, to low I"ve been having better luck. I will continue to monitor the unit. Thanks for you help.

See Answer In Context

5 Replies 5
BillP
Administrator Administrator
Administrator
0 Likes
0
341

Re: APC 1500 smartups outlet groups

This reply was originally posted by Bill on APC forums on 4/18/2016


Hi,

What is the exact model number of the unit? You will find the information on a bar code stick on the back of the Smart-UPS.

When the power is cut to the outlet groups is anything logged? Also, is there anything attached to the unit via USB or Serial?

Attachments
BillP
Administrator Administrator
Administrator
0 Likes
0
341

Re: APC 1500 smartups outlet groups

This reply was originally posted by tgreene on APC forums on 4/18/2016


UPS Network Management Card 2

Model: Smart-UPS X 1500
SKU: SMX1500RM2UNC
Serial Number: AS1545213491
Firmware Revision: UPS 09.1 (ID20)
Manufacture Date: 11/05/2015
 
Apparent Power Rating: 1440 VA
Real Power Rating: 1200 W
 
Internal Battery SKU: APCRBC115
External Battery SKU: SMX48RMBP2U
 
   

BillP
Administrator Administrator
Administrator
0 Likes
0
341

Re: APC 1500 smartups outlet groups

This reply was originally posted by tgreene on APC forums on 4/18/2016


Hi, there is nothing attached to the USB or serial ports. There is nothing logged, no transfer to battery, or low volt. I did change the sensitivy to low.

BillP
Administrator Administrator
Administrator
0 Likes
0
341

Re: APC 1500 smartups outlet groups

This reply was originally posted by Bill on APC forums on 4/18/2016


Hi,

If the issue is only happening with 1 unit it is possible the unit needs to be replaced. You should verify that there is not a power down scheduled on the NMC and that there is nothing configured for load shedding. Of course those events should be logged so I do not expect you will find a scheduled shutdown or load shedding. Some thing that could cause the issue is an over load. If the unit is over loaded it could shutdown abruptly. 

BillP
Administrator Administrator
Administrator
0 Likes
0
342

Re: APC 1500 smartups outlet groups

This reply was originally posted by tgreene on APC forums on 4/18/2016


Hi,

The issue has happened on multiple units at that location. There is not a power down schedule, or load shedding. I did check the unit for an overload condition, that doesn't appear to be the case. Since I changed the sensitivity, to low I"ve been having better luck. I will continue to monitor the unit. Thanks for you help.