Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79344members
344036posts

AP9631 not upgradeable and now unuseable

Solved
ggzengel_apc
Cadet
0 Likes
4
249

AP9631 not upgradeable and now unuseable

This was originally posted on APC forums on 9/5/2015


Upgrade failed with ERROR --> Boot Monitor transfer failed.

Now it has replaced Application Module with bootmon and didn't work anymore.

Hardware Factory
---------------
Model Number:         AP9631
Serial Number:         5A1250T08561
Hardware Revision:     05
Manufacture Date:     12/15/2012
MAC Address:         00 C0 B7 9D 9E 8B
Management Uptime:     0 Days 0 Hours 1 Minute

Application Module
---------------
Name:             bootmon
Version:         v1.0.8
Date:             Apr  8 2014
Time:             10:59:40

APC OS(AOS)
---------------
Name:             aos
Version:         v5.1.7
Date:             Nov 22 2011
Time:             09:53:57

APC Boot Monitor
---------------
Name:             bootmon
Version:         v1.0.2
Date:             Jan 21 2010
Time:             13:35:57

Tags (3)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
249

Re: AP9631 not upgradeable and now unuseable

This reply was originally posted by Angela on APC forums on 9/8/2015


Yes, I recommend trying this upgrade via BootMonitor mode to resolve. Do bootmonitor .bin file first, then AOS bin file, and then the application .bin file (whatever it may be - sumx, sy, etc). The instruction details Terry linked should be helpful for via BootMonitor/XMODEM on NMC2.

See Answer In Context

4 Replies 4
Terry_Kennedy_apc
Commander
Commander
0 Likes
0
249

Re: AP9631 not upgradeable and now unuseable

This was originally posted on APC forums on 9/5/2015


The directory where you unpacked the firmware update should contain 3 .bin files - the bootmon, aos, and app (which will have different names depending on what device the firmware is intended for).

FTP to the card, make sure you're in binary mode, and do a "put" of the bootmon file. Disconnect and the NMC should reboot. After it reboots, FTP to it again, also in binary mode, and "put" the aos file. Disconnect and wait for the reboot. Repeat with the app file.

ggzengel_apc
Cadet
0 Likes
0
249

Re: AP9631 not upgradeable and now unuseable

This was originally posted on APC forums on 9/6/2015


That's what I tried beside windows update tool, too.

It doesn't matter which file I use. I get round about 20 hashes (every time the exactly same length) and after a few minutes I get a timeout and the NMC is rebooting.

I have read about AP9630 and that there was a charge which could not be updated. Wrong flash bit set or something else?

I sill formated the NMC and tried to update manually with linux and ftp on console. bin and passive or active.

Terry_Kennedy_apc
Commander
Commander
0 Likes
0
249

Re: AP9631 not upgradeable and now unuseable

This was originally posted on APC forums on 9/6/2015


The upgrade issue was for cards produced for a few weeks in 2010. Yours seems to be from late 2012.

You could try one of the other upgrade methods (USB or serial XMODEM) mentioned in FA156047. Note that that article is a generic one for 3 generations of NMC. Make sure you are following the instructions for the AP9630/1.

BillP
Administrator Administrator
Administrator
0 Likes
0
250

Re: AP9631 not upgradeable and now unuseable

This reply was originally posted by Angela on APC forums on 9/8/2015


Yes, I recommend trying this upgrade via BootMonitor mode to resolve. Do bootmonitor .bin file first, then AOS bin file, and then the application .bin file (whatever it may be - sumx, sy, etc). The instruction details Terry linked should be helpful for via BootMonitor/XMODEM on NMC2.