APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:14 AM . Last Modified: 2024-02-29 11:27 PM
We're having a strange problem with all of our AP9630 NMC2 that are running firmware v6.x. We have them configured to send e-mail notifications for all events. Although the notifications are being sent successfully, the message being sent is always one event behind the actual event that occurred.
For example, if I log in via telnet/CLI, a notification of the login should be sent. Instead, the notification contains the message of the previous event, which might have been (for example) an NTP update that occurred the day before. When I log out, the login notification will be sent (one event behind what actually occurred). The next day, when a self-test runs, the first notification message will be the logout from the day before.
We tried updating to the latest v6.2.1, but the problem continues.
We do not have this problem on any NMC2 running v5.x.
Has anyone else had this problem? Any chance that it will be fixed in the next firmware release?
Thanks in advance for any help!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:15 AM . Last Modified: 2024-02-29 11:26 PM
Thanks very much! I tried the new firmware on one of our problem units, and confirmed that it resolves the sending / notification problem.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:14 AM . Last Modified: 2024-02-29 11:27 PM
Hi Robert,
I had logged a bug on this a few months ago and have brought visibility to it. It is on the top of my own personal list to drive to resolution. Not everyone sees this issue but I have not heard of a root cause yet. I also haven't been able to figure out what the commonality is across everyone who sees it. I will add your information to our bug detail and continue to voice the urgency on getting this resolved.
For reference, here is another thread on the issue: http://forums.apc.com/spaces/7/ups-management-devices-powerchute-software/forums/general/10465/ap963... and I think there maybe another one somewhere.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:14 AM . Last Modified: 2024-02-29 11:27 PM
Thanks for your reply and for your attention to this problem. Glad to see it is getting some attention.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:14 AM . Last Modified: 2024-02-29 11:27 PM
Since a fix doesn't seem to be coming any time soon, how would we go about downgrading to a prior firmware version? It seems that 6.1.1 is OK and does not have the e-mail / notification bug. Anything 6.2 or later has the problem. Only 6.2.1 is available on the support web site, is there some way to get the earlier versions and to apply them as a downgrade? Can I use FTP to extract the needed files from an NMC2 card running 6.1.1 and apply them to a card currently running 6.2.1?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:14 AM . Last Modified: 2024-02-29 11:27 PM
Minor correction to last post: 6.1.1 *does* seem to have the bug. How do we downgrade to 5.x?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:14 AM . Last Modified: 2024-02-29 11:27 PM
Hi Angela,
Thanks for attaching the v517 files for the NMC2 downgrade. I read through the support articles you referenced, and I **think** I understand the downgrade process as follows:
1) Use FTP to transfer the AOS file first. QUESTION: What happens to the v611 AOS file, do I have to manually delete it? QUESTION: Do I have to manually initiate a reboot of the NMC2 card, or is that somehow automatic?
2) Use FTP to transfer the sumx file. QUESTIONS: Same as above, do I have to manually delete the v611 sumx file, and do I have to manually reboot the management card?
3) Format (wipe flash) and reconfigure all settings.
Thanks for your help with these questions.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:14 AM . Last Modified: 2024-02-29 11:26 PM
Hi Robert,
1.) Yes, all you need to do is FTP new AOS. The card does the rest including knowing to reboot when AOS transfer is complete.
2.) Yes, all you need to do is FTP the APP second. Same as above regarding reboot.
3.) Yes, do that after - you're correct.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:15 AM . Last Modified: 2024-02-29 11:26 PM
Hi,
I'm experiencing the same issue, but on AP9537SUM Network Card. Is there any update about the solution. Can I find firmware upgrade for my product? (on website I just foud firmware for AP9630/9631 models).
Thank you in advance,
Federico
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:15 AM . Last Modified: 2024-02-29 11:26 PM
Hi Angela,
We are experiencing this issue at 2 of our 6 locations. I would be happy to post logs or send you anything else that might help. Otherwise, if there's any update to this problem, can you share?
Thanks!
-Matt
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:15 AM . Last Modified: 2024-02-29 11:26 PM
Hi Matt,
I checked into the bug I had logged earlier this year. From what I am hearing and seeing, we have resolved the issue with any NMC2 applications that have AOS (APC OS) 6.3.3 or higher. This will start being released for a few different applications late this year/early next year. If you can tell me which specific applications you have (Smart-UPS, Rack PDU, Symmetra, etc), I can possibly give you a more specific ETA. (The newest AOS out there as "final" today I think is only AOS 6.3.2 for certain applications.)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:15 AM . Last Modified: 2024-02-29 11:26 PM
On 10/13/2015 5:56 PM, Angela said:Hi Matt,
I checked into the bug I had logged earlier this year. From what I am hearing and seeing, we have resolved the issue with any NMC2 applications that have AOS (APC OS) 6.3.3 or higher. This will start being released for a few different applications late this year/early next year. If you can tell me which specific applications you have (Smart-UPS, Rack PDU, Symmetra, etc), I can possibly give you a more specific ETA. (The newest AOS out there as "final" today I think is only AOS 6.3.2 for certain applications.)
Sure thing. We're using Smart-UPS with the AP9630.
Thanks!
-Matt
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:15 AM . Last Modified: 2024-02-29 11:26 PM
This issue sounds similar if not the same problem as:
https://community.exchange.se.com/t5/Datacenter-Forum/bd-p/datacenter-forum.
This seems to effect the transmission of e-mails period. Also access to the Management console as well.
I am awaiting since March for these issues to be resolved, with no news. Waiting for FW update for my 9630's (Smart-UPS)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:15 AM . Last Modified: 2024-02-29 11:26 PM
Any news on an AOS 6.3.3 release for AP9630 NMC2 on Smart UPS 2200? It seems to be available only for the Symmetra.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:15 AM . Last Modified: 2024-02-29 11:26 PM
I just tested the latest 6.4 firmware and it fixed this issue for us.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:15 AM . Last Modified: 2024-02-29 11:26 PM
Hi Angela,
Do you possibly have the release notes/bug fixes for V6.4.0?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:15 AM . Last Modified: 2024-02-29 11:26 PM
Hi,
I don't see the final copy yet. It is in the last stages of release/cleaning. Potentially why the download hasn't been posted yet since they will be posted as well.
Some high level fixes/enhancements off the top of my head:
If you have a specific question/issue you want to know about, I can check into it.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:15 AM . Last Modified: 2024-02-29 11:26 PM
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:15 AM . Last Modified: 2024-02-29 11:26 PM
Firmware now posted! I made a post on this site here with links and FYIs: http://forums.apc.com/spaces/7/ups-management-devices-powerchute-software/forums/general/11714/fyi-u...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:15 AM . Last Modified: 2024-02-29 11:26 PM
Thanks very much! I tried the new firmware on one of our problem units, and confirmed that it resolves the sending / notification problem.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.