APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:45 AM . Last Modified: 1 month ago
I have 11 AP9619 UPS's, of which I could upgrade the firmware on 4 without issue.
The remaing ones are all failing the firmware upgrade with the "Could not log intothe cards FTP server" error.
I can log into the devices, Telnet to the devices and FTP in with the credentials provide.
Help ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:45 AM . Last Modified: 1 month ago
Hi Lloyd,
Only if you currently have AOS 1.X.X, you need to to AOS 2.0.2 then from there, you can go to whatever version you want. I saw in your screenshot, you already have 3.2.1 which is fine so you can skip 2.0.2.
You'll want to push AOS 3.7.3, disconnect, let the NMC reboot, then sumx 3.7.2, then disconnect, let the NMC reboot, and you're all set
Let me know if you need any clarification.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:45 AM . Last Modified: 1 month ago
Hi Lloyd,
No worries, we should be able to address this pretty easily.
I see you're trying to load firmware on the AP9619 Network Management Card for a single phase Symmetra model UPS though you have Smart-UPS firmware currently on the NMC in the screenshot. Is that intentional? I just want to make sure before proceed that we have the right firmware. Please confirm what model of UPS the AP9619 management card is installed in.
Anyway, I think that we should try via FTP manually and not use the wizard. That method is outlined here and refer to NMC1 FTP -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156047
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:45 AM . Last Modified: 1 month ago
The devices are single phase 208V Smart-UPS 5000 XL with Attached step down transformer and additionla battery pack.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:45 AM . Last Modified: 1 month ago
One additional qurestion
There are two aos files in the firmware folder:
apc_hw02_aos_202.bin
apc_hw02_aos_373.bin
in addition to the sumx bin file.
Do both aos bin's get uploaded ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:45 AM . Last Modified: 1 month ago
Hi Lloyd,
Only if you currently have AOS 1.X.X, you need to to AOS 2.0.2 then from there, you can go to whatever version you want. I saw in your screenshot, you already have 3.2.1 which is fine so you can skip 2.0.2.
You'll want to push AOS 3.7.3, disconnect, let the NMC reboot, then sumx 3.7.2, then disconnect, let the NMC reboot, and you're all set
Let me know if you need any clarification.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.