APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:25 AM . Last Modified: 1 week ago
We are going to perform a firmware upgrade on an AP8841 PDU. Is there any risk of losing power during the upgrade and reboot?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:25 AM . Last Modified: 1 week ago
Hi Scott,
Only the NMC will reboot not the whole PDU, there should be no impact on the load.
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:25 AM . Last Modified: 1 week ago
Hi Scott,
Only the NMC will reboot not the whole PDU, there should be no impact on the load.
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.