AP7922 circuit breaker trip notification?

This was originally posted on APC forums on 11/24/2009


Is there any kind of notification or alert if the circuit breaker on a AP7922 PDU trips?

We had this happen at a remote site and all the LED's were still green and the command line interface did not give any indication of the circuit breaker being tripped?

Thanks,E


Accepted Solutions
Erasmus_apc
Sisko
Sisko
0 Likes
0
127

Re: AP7922 circuit breaker trip notification?

This was originally posted on APC forums on 11/30/2009


There is no way to notify users if a breaker trips, explicitly. However, you can set notifications for "Low Load" warnings. Setting these to alarm at 0 load basically does the same thing, since the unit will be informing you the load has gone to 0 amps, i.e. dropped. You can accomplish this in the Administration -> Notification section of the RPDU web GUI.

See Answer In Context

1 Reply 1
Erasmus_apc
Sisko
Sisko
0 Likes
0
128

Re: AP7922 circuit breaker trip notification?

This was originally posted on APC forums on 11/30/2009


There is no way to notify users if a breaker trips, explicitly. However, you can set notifications for "Low Load" warnings. Setting these to alarm at 0 load basically does the same thing, since the unit will be informing you the load has gone to 0 amps, i.e. dropped. You can accomplish this in the Administration -> Notification section of the RPDU web GUI.