Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79098members
343434posts

AP7922 circuit breaker trip notification?

Solved
Moonf4_apc
Crewman
Crewman
0 Likes
1
122

AP7922 circuit breaker trip notification?

This was originally posted on APC forums on 11/24/2009


Is there any kind of notification or alert if the circuit breaker on a AP7922 PDU trips?

We had this happen at a remote site and all the LED's were still green and the command line interface did not give any indication of the circuit breaker being tripped?

Thanks,E


Accepted Solutions
Erasmus_apc
Sisko
Sisko
0 Likes
0
122

Re: AP7922 circuit breaker trip notification?

This was originally posted on APC forums on 11/30/2009


There is no way to notify users if a breaker trips, explicitly. However, you can set notifications for "Low Load" warnings. Setting these to alarm at 0 load basically does the same thing, since the unit will be informing you the load has gone to 0 amps, i.e. dropped. You can accomplish this in the Administration -> Notification section of the RPDU web GUI.

See Answer In Context

1 Reply 1
Erasmus_apc
Sisko
Sisko
0 Likes
0
123

Re: AP7922 circuit breaker trip notification?

This was originally posted on APC forums on 11/30/2009


There is no way to notify users if a breaker trips, explicitly. However, you can set notifications for "Low Load" warnings. Setting these to alarm at 0 load basically does the same thing, since the unit will be informing you the load has gone to 0 amps, i.e. dropped. You can accomplish this in the Administration -> Notification section of the RPDU web GUI.