Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
You can subscribe to this forum after you log in or create your free account..
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
Posted: 2021-06-28 12:15 AM
This question was originally posted by Alessandr on APC forums on 4/3/2017
Hi. I've got a problem with an ATS model AP7721, it doesn't show current or load when the A source is active.
First I thought that was a firmware issue so I run an firmware update. This is the current version
Model: | AP7721 |
Firmware Revision: | 3.0.7 |
Firmware Date: | 03/10/16 |
Hardware Revision: | R01 |
Manufacture Date: | 08/07/2014 |
Serial Number: | 5A1432T04685 |
Source Measurements | ||||
Source A | Source B | |||
Input Frequency: | 50 | Hz | 50 | Hz |
Input Voltage: | 218 | VAC | 217 | VAC |
Power Output and Power Supplies | ||||
Power Output | ||||
Total Power: | 0 | Watts | ||
Power Supplies | ||||
Source A 24V PS: | 23 | VDC | ||
Source B 24V PS: | 23 | VDC | ||
+12V PS: | 12 | VDC | ||
-12V PS: | -12 | VDC | ||
5V PS: | 5 | VDC |
Then I saw that some others ATS work ok and I found that if the source A is active the ATS doesn't show any measure. If source B is active it's show the measure ok.
Any help or idea to solve this problem??
Thanks in advance.
Posted: 2021-06-28 12:15 AM
This reply was originally posted by Angela on APC forums on 4/4/2017
OK, thanks. I was just checking because a complete power off is not normally needed for a firmware upgrade on these products...
Posted: 2021-06-28 12:15 AM
This reply was originally posted by Angela on APC forums on 4/3/2017
Hello,
This unit appears to have been manufactured in 2014 - did you recently purchase it? If not, how long has it been in service? I am curious if this ever worked for you.
When source B is working properly, how much current is it able to detect?
I would think it is a hardware problem somewhere with the circuitry that is used to detect the current on the particular source but it is possible if the load is extremely low, sometimes it won't be able to read it.
Lastly, the event.txt and data.txt would be helpful to review, especially with the specifics about if this ever worked properly. Instructions are located here are downloading event.txt and data.txt (config.ini is not needed at this time) -> http://www.apc.com/us/en/faqs/FA156131
Posted: 2021-06-28 12:15 AM
This reply was originally posted by Alessandr on APC forums on 4/4/2017
Angela thanks for you reply.
We bought them on 2014, but we start to installed in 2016. These ats were working for around one year.
A few months ago I configured with SNMP and syslog to control them and I found this problem.
This morning I was doing a more detailed work and I found that after the firmware update (3.07) a completely shutdown of the ats seems to be the solution.
I' ve installed 7 ATS and at this time 3 have problems, but the problem is different, they report 0A
ATS-01 firmware 3.07 hardware R01. This ats is reporting a 0A load, but It has got connected a HP desktop PC and 5 modems.
ATS-02 firmware 3.07 hardware R01. This ats is reporting a 0A load, but It has got connected a netbackup tape library, I'm not sure about the load of this equipment.
ATS-03 firmware 3.05 hardware R01 This ats is reporting a 0A load but it's has got connected 2 switches FC brocade.
I will go on working to solve this problem.
Thanks
Posted: 2021-06-28 12:15 AM
This reply was originally posted by Angela on APC forums on 4/4/2017
Hi Alessandr,
Thanks for the update. So you're saying after you upgraded the firmware, a complete power down of the ATS fixed the issue? So you'll go and turn all of the others on and off?
Posted: 2021-06-28 12:15 AM
This reply was originally posted by Alessandr on APC forums on 4/4/2017
Yes. There are 3 ATS that still not work, I think this is because I am not be able to power off them due to critical equipment.
I'll update the post as soon as possible.
Regards
User | Count |
---|---|
4834 | |
190 | |
111 | |
108 | |
67 | |
63 |
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.