Posted: 2021-07-01 03:13 AM . Last Modified: 3 weeks ago
The APC 9631 network management card with current firmware 5.1.7 outputs the wrong SNMP temperature values if the Temperature Scale preference (Administration> General> Preferences> Temperature Scale:) is set to Fahrenheit for web GUI Environment display.
Per the MIBs SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.5 should always result in temperature display in Fahrenheit and SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.6 should always result in Celsius.
When set to Celsius:
snmpwalk [hostname] -v1 -c public .1.3.6.1.4.1.318.1.1.25.1.2
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.1.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.1.2.1 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.2.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.2.2.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.3.1.1 = STRING: "Port 1 Temp 1"
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.3.2.1 = STRING: "Port 2 Temp 2"
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.4.1.1 = STRING: "Port 1"
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.4.2.1 = STRING: "Port 2"
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.5.1.1 = INTEGER: 77
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.5.2.1 = INTEGER: 77
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.6.1.1 = INTEGER: 25
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.6.2.1 = INTEGER: 25
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.7.1.1 = INTEGER: 38
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.7.2.1 = INTEGER: -1
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.8.1.1 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.8.2.1 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.9.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.9.2.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.10.1.1 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.10.2.1 = INTEGER: 2
When set to Fahrenheit:
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.1.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.1.2.1 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.2.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.2.2.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.3.1.1 = STRING: "Port 1 Temp 1"
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.3.2.1 = STRING: "Port 2 Temp 2"
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.4.1.1 = STRING: "Port 1"
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.4.2.1 = STRING: "Port 2"
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.5.1.1 = INTEGER: 171
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.5.2.1 = INTEGER: 172
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.6.1.1 = INTEGER: 77
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.6.2.1 = INTEGER: 78
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.7.1.1 = INTEGER: 38
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.7.2.1 = INTEGER: -1
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.8.1.1 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.8.2.1 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.9.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.9.2.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.10.1.1 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.10.2.1 = INTEGER: 2
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 03:13 AM . Last Modified: 3 weeks ago
we had an issue with this but it was fixed already over a year ago where a double calculation was being performed depending on the preference setting. I know you said this was version 5.1.7 firmware but can you please provide a screenshot of the firmware versions from the web interface under Administration->General->About please.
I just double checked this on my end for sanity's sake knowing it was a non issue these days and verified my temp preference was on Celsius and I am seeing 82 for uioSensorStatusTemperatureDegF and 28 for uioSensorStatusTemperatureDegC as I expect to.
Here is what I am running per sysDescr (.1.3.6.1.2.1.1.1) OID under mib-2 which maybe you can get that instead for me: APC Web/SNMP Management Card (MB:v4.0.1 PF:v5.1.7 PN:apc_hw05_aos_517.bin AF1:v5.1.7 AN1:apc_hw05_sumx_517.bin MN:AP9631 HR:05 SN: BA08XXXXXXX MD:01/16/2009) (Embedded PowerNet SNMP Agent SW v2.2 compatible)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 03:13 AM . Last Modified: 3 weeks ago
we had an issue with this but it was fixed already over a year ago where a double calculation was being performed depending on the preference setting. I know you said this was version 5.1.7 firmware but can you please provide a screenshot of the firmware versions from the web interface under Administration->General->About please.
I just double checked this on my end for sanity's sake knowing it was a non issue these days and verified my temp preference was on Celsius and I am seeing 82 for uioSensorStatusTemperatureDegF and 28 for uioSensorStatusTemperatureDegC as I expect to.
Here is what I am running per sysDescr (.1.3.6.1.2.1.1.1) OID under mib-2 which maybe you can get that instead for me: APC Web/SNMP Management Card (MB:v4.0.1 PF:v5.1.7 PN:apc_hw05_aos_517.bin AF1:v5.1.7 AN1:apc_hw05_sumx_517.bin MN:AP9631 HR:05 SN: BA08XXXXXXX MD:01/16/2009) (Embedded PowerNet SNMP Agent SW v2.2 compatible)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 03:13 AM . Last Modified: 3 weeks ago
My bad - of the many, MANY smart-UPS' that we are monitoring, the ones with the problem are NOT running 5.1.7. I inadvertently checked firmware on 3 that were not having the problem. Thanks much.