Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79150members
343588posts

9630's running 6.4 and SMT's (various) all at latest firmware - display and schedule questions

Solved
Charlieojs_apc
Crewman
Crewman
0 Likes
4
118

9630's running 6.4 and SMT's (various) all at latest firmware - display and schedule questions

This was originally posted on APC forums on 1/28/2016


Long time since I have been on the forum....so I hope I picked the correct section for my questions.

We have 15 SMT devices ranging in size from 750 to 3000 and in age from 4 years old to new. Each has a 9630 NMC 2 installed. I spent yesterday updating all the NMC's to 6.4 and then all the SMT's to their latest firmware (where needed/available). Wow, has the process improved! I do not run any network software and rely on email reporting from the NMC's for managing each device.

I am wanting to set all the SMT displays to turn off, rather than dim. Do I really need to go to each unit again and manually make the change on the front panel? Why isn't that an option (adjust panel display) on the NMC2? Did I miss that somewhere? Seems like this setting would be a natural for the NMC2.

Second question. Is it possible to synchronize my weekly test schedule among devices? In other words, I want all 15 devices to run their weekly battery load test every Tuesday. Can be anytime on Tuesday. I don't see an easy way to accomplish this without operating all devices on battery until they "die" and then powering everything back up on the same day..... My thinking is that I want to ID any battery issues as early in the week as possible and all at the same time (so I can task the repairs to folks I know can get it done).

Angela and folks, your advice is always appreciated!

Charlie


Accepted Solutions
Charlieojs_apc
Crewman
Crewman
0 Likes
0
118

Re: 9630's running 6.4 and SMT's (various) all at latest firmware - display and schedule questions

This was originally posted on APC forums on 1/29/2016


Correct. There are numerous reasons why the current NMC2 setting don't work for us .... in a relatively short period of time, the day/time when the test runs, changes ..... for any number of reasons. 

See Answer In Context

4 Replies 4
BillP
Administrator Administrator
Administrator
0 Likes
0
118

Re: 9630's running 6.4 and SMT's (various) all at latest firmware - display and schedule questions

This reply was originally posted by Bill on APC forums on 1/28/2016


Hi,

On 1/28/2016 4:20 AM, Charlie said:

I am wanting to set all the SMT displays to turn off, rather than dim. Do I really need to go to each unit again and manually make the change on the front panel? Why isn't that an option (adjust panel display) on the NMC2? Did I miss that somewhere? Seems like this setting would be a natural for the NMC2.

This has been added as an enhancement request for a future release. 

On 1/28/2016 4:20 AM, Charlie said:

Second question. Is it possible to synchronize my weekly test schedule among devices? In other words, I want all 15 devices to run their weekly battery load test every Tuesday.

The NMC does not offer this as a setting however, you can do this via command line. I suggest changing the seft-test setting to only run at start up. Then write a script that will run remotely each Tuesday telling the NMC to run the self-test. For help with the command line see Command Line Interface Guide. Another option is write a command script that triggers the self-test using SNMP. 

Charlieojs_apc
Crewman
Crewman
0 Likes
0
118

Re: 9630's running 6.4 and SMT's (various) all at latest firmware - display and schedule questions

This was originally posted on APC forums on 1/29/2016


Bill,

I am familiar with the command line interface. Used it too many times back in the day with our first gen NMC's. Using it makes me nostalgic for my CP/M days 🙂

I really don't want to write a script that runs from our network. Seems like an unnecessary complication that I don't want to deal with and manage. If we can't do this from our cards, then I will pass and add it to my wish list for APC. I really do think it makes sense as a load test option ...... where there are multiple devices on a network.

Charlie

mitsmith_apc
Lt. Commander
Lt. Commander
0 Likes
0
118

Re: 9630's running 6.4 and SMT's (various) all at latest firmware - display and schedule questions

This was originally posted on APC forums on 1/29/2016


Hi Charlie,

A back way that seems to work for your self test schedule issue is to manually run a self test at the time you want it to occur in the future. The NMC will run its automatic self test 7 or 14 days (depending on your setting) from when the last self test was run. It is not a permanent solution though as if the unit ever turns off or you run other manual self tests it will throw off the automatic self test schedule. 

Hopefully this helps!

-Mike

Charlieojs_apc
Crewman
Crewman
0 Likes
0
119

Re: 9630's running 6.4 and SMT's (various) all at latest firmware - display and schedule questions

This was originally posted on APC forums on 1/29/2016


Correct. There are numerous reasons why the current NMC2 setting don't work for us .... in a relatively short period of time, the day/time when the test runs, changes ..... for any number of reasons.