1000rm2u *supposed* to be hot to the touch?

Solved
iefbr14_apc
Cadet
0 Likes
3
114

1000rm2u *supposed* to be hot to the touch?

This was originally posted on APC forums on 11/22/2009


it is hot, as in i can't hold my hand against it for longer than a few seconds.... wanting to make sure this is normal. batteries indicate fully charged, and disconnecting from shore power results in failover to battery (so the thing appears operational).

thanks

Tags (1)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
114

Re: 1000rm2u *supposed* to be hot to the touch?

This reply was originally posted by Jonathan on APC forums on 11/23/2009


Jim,

What is the model and serial number of the UPS? The batteries that are on the UPS, are they the original ones that came with the unit? When did this problem started? Also, would it be possible for you to open the battery compartment to check its condition, check for signs of swelling, bulging, venting or leaks. Also, see if you can still remove the batteries from the unit itself.

JonPro

See Answer In Context

3 Replies 3
BillP
Administrator Administrator
Administrator
0 Likes
0
114

Re: 1000rm2u *supposed* to be hot to the touch?

This reply was originally posted by Vkooldog on APC forums on 11/23/2009


Hi,

If your batteries are too hot to touch, it means that the deployment conditions of that unit may not be suitable. A raise in temperature will shorten the lifespan of the UPS ( compoments ) and the batteries life.

What I would suggest is to move the unit to a more cooler environment and monitor its internal temperature thru APC software and take steps to keep the environment temperature of the UPS to its operating environment eg below 25 degress Celcius.

Regards


Message was edited by: kooldog007

Message was edited by: kooldog007

BillP
Administrator Administrator
Administrator
0 Likes
0
114

Re: 1000rm2u *supposed* to be hot to the touch?

This reply was originally posted by Vkooldog on APC forums on 11/23/2009


If your batteries are too hot to touch, it means that the deployment conditions of that unit may not be suitable. A raise in temperature will shorten the lifespan of the UPS ( compoments ) and the batteries life.

What I would suggest is to move the unit to a more cooler environment and monitor its internal temperature thru APC software and take steps to keep the environment temperature of the UPS to its operating environment eg below 25 degress Celcius.

Regards

BillP
Administrator Administrator
Administrator
0 Likes
0
115

Re: 1000rm2u *supposed* to be hot to the touch?

This reply was originally posted by Jonathan on APC forums on 11/23/2009


Jim,

What is the model and serial number of the UPS? The batteries that are on the UPS, are they the original ones that came with the unit? When did this problem started? Also, would it be possible for you to open the battery compartment to check its condition, check for signs of swelling, bulging, venting or leaks. Also, see if you can still remove the batteries from the unit itself.

JonPro