I am getting a compensating for high voltage on only 1 unit in my facility. but the voltage is not exceeding the threshold of 127.
thoughts?
0x010D
Serial Number :
Device Serial Number :
Date : 04/23/2016
Time : 22:29:37
Code : 0x010D
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:31 PM . Last Modified: 3 weeks ago
Alan,
127 is a low setting and I see that there are a few entries in the data log at 125.19 so it is possible the voltage bumped up higher. Set the threshold to 130 and monitor it. That should resolve the issue.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:30 PM . Last Modified: 3 weeks ago
Alan,
What is the exact model Smart-UPS? You will find the information on the bar code stick on the back of the unit.
Also, is there a network management card in the UPS? If there is it would be helpful to review the data and event logs.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:30 PM . Last Modified: 3 weeks ago
serial number ZA1544070185
device serial 3S1550X01309
its a UPS 1000/1500VA
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:30 PM . Last Modified: 3 weeks ago
Alan,
Is there a network card in the Smart-UPS. It would be helpful to see the event and data logs. Also, what is the exact model number? Examples: SMT1000, SMX1000
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:31 PM . Last Modified: 3 weeks ago
Notice the threshold isn't passing the 127 and it triggers high voltage.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:31 PM . Last Modified: 3 weeks ago
Alan,
127 is a low setting and I see that there are a few entries in the data log at 125.19 so it is possible the voltage bumped up higher. Set the threshold to 130 and monitor it. That should resolve the issue.