Posted: 2022-05-21 05:25 AM
I have an SRT5KRMXLI (APC Smart-UPS On-Line) that the firmware update failed on and now has no web interface. The forum post I followed (which I've now lost) said that the 704 updater was the correct one for this model - possibly this was not the case.
When I attempt to connect to the web UI, I get an "The Application Was Not Able to Load" message. I can log in via telnet which presents me with an AOS v6.7.2 interface, and I can see that there is still a apc_hw05_aos_672.bin present.
Please can someone suggest:
A) How I can restore the web interface functionality
B) How I can find the latest supported firmware for the device?
Many thanks!
Posted: 2022-05-31 07:14 AM
I found the required help guide, more by good luck than good judgement:
https://www.apc.com/us/en/faqs/FA293874/
It did require purchasing of a serial to 2.5mm jack converter which is possibly the most obnoxious interface cable ever, but at least it's working again.
Posted: 2022-05-31 07:14 AM
I found the required help guide, more by good luck than good judgement:
https://www.apc.com/us/en/faqs/FA293874/
It did require purchasing of a serial to 2.5mm jack converter which is possibly the most obnoxious interface cable ever, but at least it's working again.