Hello,
Is there not a quick and dirty How To configure PowerChute Events and UPS Events?
I guess this is how it works:
In PowerChute - configure Events:
On the Battery/UPS itself, I configure:
My Conclusion – please correct if wrong
So I guess than logically it works like this:
- Mains Power is removed
- Battery -> management Network card -> notifies Powerchute Client
- Powerchute client waits till an even is triggered
- Remaining time comes under the threshold -> Powerchute start shuting down vmWare servers (Runtime exceeded )
Question: When will the last virtual server be shut down? When are the hosts (servers) shutdown?
- After some time, perhaps quicker than expected, the battery might give a message Battery Low Duration. Than what happens? Does Powerchute respond to this message? If it going to shutdown the hardware (esxi host to maintenance?)?
AND:
Is there a diagram / flow on how events occur and where to configure?
Do I need to trial and error?
Sorry, I find the manuals individual not very clear on the events and the combination of ups and powerchute is for none-APC person not easy to understand.
Any feedback that is correct, welcome!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-27 11:35 AM
When the Shutdown Action is enabled for an event, PowerChute treats the event as critical and will trigger a shutdown sequence. Shutdown is not supported for all events: this is indicated by the presence or absence of the shutdown icon on the event row.
The Delay field is the amount of time in seconds that PowerChute should wait before initiating the shutdown sequence.
By default, PowerChute will trigger a shutdown sequence if a low battery condition occurs or the UPS is commanded to turn off. Shutdown cannot be disabled for these events using the PowerChute user interface.
On the Battery/UPS itself, I configure:
Below is from the Network card help file
My Conclusion – please correct if wrong
So I guess than logically it works like this:
- Mains Power is removed
- Battery -> management Network card -> notifies Powerchute Client. Correct
- Powerchute client waits till an even is triggered Or the UPS signals low battery
- Remaining time comes under the threshold -> Powerchute start shuting down vmWare servers (Runtime exceeded ) If configured to do so yes.
Question: When will the last virtual server be shut down? When are the hosts (servers) shutdown?
See the PowerChute VMware User's Guide starting on page 163
- After some time, perhaps quicker than expected, the battery might give a message Battery Low Duration. Than what happens? Does Powerchute respond to this message?
By default, PowerChute will trigger a shutdown sequence if a low battery condition occurs or the UPS is commanded to turn off. Shutdown cannot be disabled for these events using the PowerChute user interface.
If it going to shutdown the hardware (esxi host to maintenance?)? Yes
Is there a diagram / flow on how events occur and where to configure?
Diagrams are available starting on page 113 of the PowerChute VMware User's Guide
We also have published Application Note 180 and I have attached a copy to this post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-09-01 11:28 PM
Thank you! Will look into that soon. Very helpful since I find the given help often not so clear.