Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
NMC AP9630 reconfiguration
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-05-2307:28 AM. Last Modified: 2022-05-2307:37 AM
NMC AP9630 reconfiguration
NMC AP9630 in SMX1500RM2UNCQ. Took in as trade, accessed briefly via https but with protest (Firefox), was booted from web Ui while changing name, contact, etc. from previous owner. Now cannot access web interface on http or https - can communicate via SSH.
Question I have is will a factory reset cause new certificate generation (which is what all web browsers seem to be complaining about), or do I have to use the format command and reset? Will format put me back at initial installation stage (which is what I want at this point)?
Obviously I would rather use the web Ui as it is easier and faster so what must I do to get access via web Ui restored?
I can provide UPS serial if requested - I do not have the serial cable as yet, but one is on the way so eventually I can go that route if needed.
To start with, kindly provide the LED status of the network management card for us to know in what state it is currently on.
Since you have just acquired the UPS/NMC, I would start by doing a firmware upgrade and then the factory reset. I have provided the FAQ's below to assist you with the process as well as the link where to find the latest firmware for the NMC.