Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
Move PowerChute software to a new server
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-0311:08 AM
Move PowerChute software to a new server
I have a Smart-UPS which is connected to a server running PowerChure via a USB cable, and now I would like to replace the server with a new one.
Is there any way to move the PowerChute installation without losing all the configuration, logs and events which would happen if I just installed it on the new one?
You can save the PowerChute EventLog, Datalog from the old system. Do a clean install of PowerChute on the new system. Stop the PowerChute service on the new system. Then replace the newly created EventLog and Datalog files with the old system and restart the PowerChute service. The new system will now display the historical Event and Data logs.
As for the configuration, that will have to be replicated manually.
Another option if you are running PowerChute Agent version 10 is to go to About, and at the bottom of the page, you can create an archive.zip. This will save your data to a zip. You can then uncompress the file and view the historical event, data, and energy usage logs with a text editor.